6 MVA transformer secondary is rated for 725V at no load.
The incommer ACB is rated at 690 V, 3200 Amp. Would there
be any effect on performance of ACB due to lower voltage
rating?
Answers were Sorted based on User's Feedback
Answer / mnm
Your selection is OK. Any breaker will have 110% voltage
withstand capability. Only thing is interruption capability
reduces, which is not relevent on no-load. On load, the
voltage of the transformer will reduce by nearly 6%, due to
impedance, making it just suitable.
Is This Answer Correct ? | 1 Yes | 1 No |
ACB is not suitable as transfomer secondary voltage level
is higher than ACB voltage level which cause insulation
failure of the ACB and cause of flash.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / loke
We can agree with Mr.Mnm because actually the rating of
breaker ia 690v and it will be having with stand capacity of
+_10% so it can with stand upto 765v & also check out with
the impedence it would be around 6-9% from that also you can
check secondary voltage of t/f.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / joe
there wil be no effect because in transformer the input and
the output is difference due to the coil winding
Is This Answer Correct ? | 1 Yes | 5 No |
in a 740 kw dc seperately excited motor field voltage is constant about 17.4 volts and armature voltage is500 volts dc. how it is possible to have two different voltages from single transformer of output voltage 500 volts? if any difficulty in question contact ajitsingh.kadian@gmail.com
why some time Railway Fan not Rotate,But after a small rotation by human then it rotate normally? Why?
We are installing a 1.6 MVA transformer at our crusher plant and the feeder of HPSEBL is 2 km away at substaion . and a VCB is installed in the substaion which is 2 km away from transformer so we need another VCB near the transformer.
Hi, We facing one similar problem in our computers i.e we are newly constructed our design department after that shifted our computers but our computer desktop screen is vibrating. we are conducted our electrical maintainance person he told that is UPS problem, then we changed the UPS also again we are facing that problem in that room only. then we put lcd monitors that problem is solved. But in other monitors why the computer desktop screen is vibrating please give a suggestion to me. Regards, Raju.N.G
how we findout a ignater is faulty or not?
How can we choose the rating of submersible motors
1) How to calculate battery backup for ups as well as solar with complete formula elaborately......
is ac supply can store
which type of cabel
may anybody tell me the names of institute where plc programing course are conducted
by using pump duty, how we will can calculate the motor duty(KW)? is there any standard or formula.
What is meant by control system?