Answer / soumendasbiswas
Depending upon the total load and maximum demand of that
plant...
| Is This Answer Correct ? | 21 Yes | 7 No |
Answer / rajani
Actually DG size has to select depends on maximum demand
and considering base load and starting load and step load
base load = total maximum demand - loads which are
taking high loads at startign
starting load = if motor loads are DOL starts 6 times to
the Ifl will take at starting and soft
starters /VFD's will take 3 times to Ifl
step load = Whwn the main power supply is off
immidiently what are the load we can
switched ON through DG -called step load
(generally 40-60% of Dg load can be ON as
first step)
So our selected DG shopuld meet the step load and capable
to withstand startign loads
| Is This Answer Correct ? | 12 Yes | 5 No |
Answer / sheo
Suppose LOAD-1000 KW
So design load of Genset @ 80% inefficiency.
and power factor @80% in case of ( Failure of capacitor)because life of Capacitor and Gen set never equal to each other.
so 100% power back-up for 1000 KW load required DG 1000/0.64=1562.5 KVA
Recommended DG-1500 KVA
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / rakesh kumar sharma
generally the efficiency of the D.G.set is 80% because of
the power factor.so u have to add 20% on the entire
load.
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / sijish
DG normaly loads up to 80% of the full load rating,
First step.Calaculate the load in KW.
Consider the staring current of the Load.
The minimum Amps rating of the dg shoul be 4 Times the
Running current of the motor load
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / anil
Depending up on the total load to select the dg.for 5kw
load 10kva DG is suitable.
dg can be loaded for 80% of full load ,ie 8kw
calculating PF 6.4 kw can be loaded in 10kva dg.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / m.prabhakar
Depending up on the total load to select the dg.For example
180KW load is there 200kva capacity genarator is sufficient.
| Is This Answer Correct ? | 23 Yes | 29 No |
What are the point of a single core cable to be earthed?
transformer is working or not with supply of DC?
what is the diff. between AVR & H.T.Stabilizer
which fault current is maximum: 3 phase short circuit, LG, LL or LLG?? why?? in one of the problems that i have solved, 3 phase short circuit current on an unloaded generator came out to be less than the LG fault current. can anybody please explain why.
Suppose i Have an Ac motor of 25Hp 1500 Rpm 50 Hz Can i run a motor 2500 Rpm by AC drives by increasing a frequency either it safe or not ....
why we used dc supply for field in dg set
0 Answers Hindusthan National Glass,
What is the power ratio between power in Star and Delta circuit?
Dear All, Pls let me know about ELR.... CBCT is using for singnal purpose... How it works.. any body can explain pls.......
what efficiency of transformer at 100% load
Why voltages are 11kv 33kv why not others?
What is the PI test stand for transformer and what is the producer to do this test?
how can we run the induction motor at 9000 rpm ,by keeping frequency constant??
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)