what is the effect if we add capacitor on DG supply, it has
any loss or benefit.
Answers were Sorted based on User's Feedback
Answer / a.kannan
The above answer is correct And what I have experienced is
whenever we put the fixed capacitor in parallel to DG , at
any moment if load falls to certain value then consequence
KVAr (inductive ) will also reduce.Due to the fixed
capacitor the available KVAr(capacitance)is excess in the
circuit.This leads to leading current in the generator
armature circuit.Armature reaction takes place with this
leading currrent that causes excess induced EMF that
results in high voltage.this high voltage reference may be
harmful to AVR of the alternator.
Is This Answer Correct ? | 20 Yes | 0 No |
Answer / arun
Alternators are normally designed at 0.8 pf lag.It is not
advisable to run DG with capacitor banks switched ON.But as
you approach to maximum loading the winding temp.may
increase leading to tripping if cooling of alternator is
not efficient.In such a case you can put ON a few capacitor
banks & monitor the pf.Maintain pf somewhere between 0.85
to 0.90 lag.Result is the current drops and so is the
alternator temperature.This we have practically done with
our DGs.
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / safeer azam
Capacitors are used to recover the reactive component of
power (part of power utilized for manetization in
windings).It does not matter the source generating the
voltage is Diesel Generator,steam-driven Alternator or any
other source generating A.C supply.Capacitors are always
beneficial on AC supply if the power-factor is maintained
below Unity (using a power-factor regulating relay), on
lagging side.If power-factor is not maintained through
regulating relays then it has the tendency to go on leading
side which means ,over magnetization of windings.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / prn
Kindly do not post nonsense answers, if require go back to
college
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / venkatasubramanian
capacitors are used for produce the inductive power, so that
we can reduce the active power. i.e, genset producing
current is low. Normally when the motor ON some magnetic
field is also produced That magnetic field consume more
current, when we use the capacitor in parallel with the
circuit. It is Balanced.
so capacitor used .9 to .95 (lead/lag) to reduce the
load(producing current) to save the fuel.
By Venkatasubramanian (VVS)
Is This Answer Correct ? | 1 Yes | 2 No |
what is the safety of VCB.
5 Answers Nagarro, Roto Power, RotoPower,
WHAT IS EXTENDED DELTA AUTOTRANSFORMER? WHERE WE USE THAT?
What is true sine wave or pure sine wave inverter?? Is it sine wave or step wave?? If it is step wave, waves with how much step is considered as pure sine wave? Is it possible to produce pure sinewave using power electronics?
should Dy11 and Dy1 group can be operated in parallel??????
What was your role in the silicon evaluation/product ramp? What tools did you use?
what is mind in cable
In case of HV test on medium voltage cables, BS is asking for 4 U0 where as IEC is asking for 3.5 U0. Can any one advise me how this 3.5 times or 4 times U0 is derived?
What is dry and wet flashover.
what is rotary ups?
how we can select a transformer based on a particular load. suppose we have 4 motors of rating 40 h.p , 50 h.p, 80 h.p & 100 h.p. then what rating of transformer we can select. urgent. pls reply
What is maximum power transfer theorem?
1.main parts of generator? what is used A-check,B-check,C- check? 2.what is FM200 system in data centers? 3.difference between pac,ahu?