What is the d/f between DOL & star delta starter & automatic
star delta starter?
Answers were Sorted based on User's Feedback
Answer / prakash
A DOL starter connects the motor terminals directly to the
power supply. Hence, the motor is subjected to the full
voltage of the power supply. Consequently, high starting
current flows through the motor. This type of starting is
suitable for small motors below 5 hp (3.75 kW). Reduced-
voltage starters are employed with motors above 5 hp.
Although DOL motor starters are available for motors less
than 150 kW on 400 V and for motors less than 1 MW on 6.6
kV. Supply reliability and reserve power generation
dictates the use of reduced voltage or not
To reduce the starting current of an induction motor the
voltage across the motor need to be reduced. This can be
done by autotransformer starter, star-delta starter or
resistor starter. Now-a-days VVVF drive used extensively
for speed control serves this purpose also.
Is This Answer Correct ? | 492 Yes | 65 No |
Answer / niranajn
in dol starte the motor is directly fed from the line and
in star delta starter ther motor is started initially from
star and later during running from delta
Is This Answer Correct ? | 348 Yes | 49 No |
Answer / suresh pulipati
In case of Star Delta starter the motor intially will run
in star connection and when 80% of rated speed picks, the
motor change over to delta connection. With this star delta
connection we are able to reduce starting current by 1/3 of
DOL starting current and starting torque also.
Is This Answer Correct ? | 226 Yes | 33 No |
Answer / cool
Whenever you start a big heavy electric motor, you need to
start it slowly to prevent the rotor overheating and
drawing an enormous current. When the windings of a 3-phase
motor are connected in STAR the current is reduced to only
root three of the normal running current that is taken when
it is connected in DELTA.
Is This Answer Correct ? | 141 Yes | 19 No |
Answer / ankur mishra(moradabad)
In DOL starter full line voltage is fed to motor which will
start motor with a shock, it also draws very high current
than rated current(around 6 times), but if we use star-
delta starter , the motor starts as a star connection later
which is converted in to delta.
using star connection the line voltage is devided in two
phase voltages, also impedence is also increased due to two
star windings which result in low starting current and low
torque which will prevent motor to run with shock.
another difference is DOL starting takes less time while
star-delta takes more time to run at rated speed.
Is This Answer Correct ? | 91 Yes | 13 No |
Answer / honey
in induction motor the torque is propotional to squre of
supply voltage in case of dol the motor directly connected
to supply so torque is more while in star delta the motor
is firstly connected to star hence voltage is reduced
torque will be less and when motor reaches its 80% of speed
it connects with delta with the help of timer then full
voltage is supplied hence less rating motor should be
started with dol but for high rating it should be with star
delta
Is This Answer Correct ? | 58 Yes | 8 No |
Answer / dipanshu singh
in dol motor is supplied full line voltage hence torque
will be more, whereas in star delta the voltage is reduced
by root 3 times hence torque reduced
Is This Answer Correct ? | 51 Yes | 15 No |
Answer / vasu.p
in dol starter the motor is directly fed from the line and
in star delta starter then motor is started initially from
star and later during running from delta
Is This Answer Correct ? | 43 Yes | 7 No |
Answer / electo man
To the point, when motor starts using DOL it takes 6 times
its rated current to just start. while in Star-Delta
starter its starting current reduces to one by root three.
Is This Answer Correct ? | 47 Yes | 18 No |
Answer / rajendra mallick
In a DOL starter motor terminals is directly connected to
starter such that initially a very high starting current is
feed to drive the motor.Dol starter is used for small
motors below 5hp because of high starting current may
damage motor winding. Dol starter using for large motor
using star delta connection,first motor run on star
connection mode upto 80% which provide low starting current
and low torque initally and after getting maximum torgue
motor operates on delta mode with high torgue.
Is This Answer Correct ? | 25 Yes | 6 No |
what is the application of dynamic Breaking resistor in inverter ? & How it works ?
What types of high speed CMOS circuits have you designed?
0 Answers Ansal Housing, IBM, Intel,
what is the difference between Power and Distribution transformers ?
Why reverse relay used
In the N-series schneider reclosers. What is the difference between current during fault time and current at tripping? This appears in the Event log in an event of a trip out.
need to make a report. Need to choose a 3phase induction motor. Load conditions motor will operate in : Maximum Load: 30 Kw Speed: 2950 rpm Ambient temp: 20 cent Supply voltage: 440V Frequency: 50Hz need to look for the safety factor when choosing the motor, went through catalouge found a few, but dont know how to choose the safety factor allowing an extra load something above 30 KW to avoid any harm.
Why is tan-delta test and capacitor measurement done on alternator?
what is difference between KW and KVA
what are the safety measure & controls in engine?
AVR is used for the Voltage regulation of the Generator using the feedback signal by exciting the field winding of the generator.But how the field winding will be excited & using what?
what is an invertor A.C.?
If o/p power is doubled by how much does the sound increase