WHY HUMMING SOUND OCCURED IN HT TRANSMMISSION LINES?
Answers were Sorted based on User's Feedback
Answer / muthukumar
Because of high voltage the air molecules surrounding the HT
line are ionised.As the HT line carries AC current the
alternating magnetic field produced will cause the ionised
molecules to vibrate resulting in humming noise.
You can also consider the case that there will not be any
humming noise in case of HVDC transmission.
Is This Answer Correct ? | 47 Yes | 2 No |
Answer / kathirvel.r
Huming sound occured in HT AC Transmission only,Not in Dc
Transmission.Because, Corona Effect occured onlly for
AC.May i correct.
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / ilononurb
this is what we called Corona Effect. this is due to water
content of the air that sorroud in the transmission lines
that carrying high voltage ionization is taking place. So
humming sound is audible in the system.
Is This Answer Correct ? | 3 Yes | 3 No |
Answer / subhash tp
The humming sound is coming from transformer
at the time of working is due the magnetic expansion
and de-expansion at the ends of transformer cores.
At the time of working the transfomer core ends are
expanding when supply voltage occures its positive half cycle
and the transformer ends are de-expanding at the time of supply voltage occures its negative half cycle .This expansion &de-expansion is making humming sound,and also this wii continue during the transformer is working.
Is This Answer Correct ? | 1 Yes | 6 No |
FLP zone Types and Details
How can calculate the efficency of the rectifier. input 240V AC, current 5 amps,P.F 0.98, Output is 54 V DC,62.6 A.
What is the Procedure for selecting a Cable, Breaker and Transformer for particular load.
What is the type of feedback used in an op- amp schmitt trigger?
what is principle operation of transformer?
Differene between KVA and KW.
what is the principle of generator , induction motor,d.c motor
why the vfd motor take current high in vfd panel then mcc panel.current in vfd panel=160A in 93%.and mcc panel it shows 130A. (132kw motor)
Is it possible that Generator trip but Turbine not trip.Give explanation.
What is the full name of one of choke less lamp BLL
What is the difference between PT for metering and PT for protection ?
What is the difference between lubricating oil and insulating Oil?