how much loading in terms of ampere can put on 5 MVA,33/11
KV TRANSFORMER having rated current 263 Amp ?????????
Answers were Sorted based on User's Feedback
Answer / sunil bhuarya
its sunil bhuarya
ans of this question is ut self in the que.
how-
5000/(root3)*11=262.43 aproxx=263
and in case of overloading it becomes 300 to 315A.
Is This Answer Correct ? | 38 Yes | 7 No |
Answer / serwox
Answer depends on what percentage overload a transformer can
accept. For a tx that can accept a 120% overload, the
current is 315A.
Is This Answer Correct ? | 20 Yes | 5 No |
Answer / pravin
Actually it depends upon designer. If we asked designer to
designed for 125% overload, he will provide cooling per
current loading on 125% overload to restrict Hot Spot Temp.
of the winding & Top oil temp. respective to max. ambient
temp.
In this case, we can provide loading of 437A in
terms of ampere on top rating with Hot spot temp & top oil
temp in control on top rating. Actually transformer has
three rating OA/FA/FA. If this transformer is OA/FA/FA then
we can provide this loading.
If it is self cooled then 263A is max. loading.
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / sunil kumar das
above answer is also correct.we can put less than full
load current.
Is This Answer Correct ? | 6 Yes | 3 No |
Answer / jayant subhash golait
If the word rated current comes,then it is actually safe n maximum permissible limit....Obviously,the machine will misbehave when crossed this limit...to save the machine or to avoid failures,extra cooling may be required that is also within tolerable range...again the manufacturer may declare that value as a rated current which is itself little bit away from tripping or breakdown or danger zone of tolerance....finally ,it is solely depend upon manufacturer n in turn the quality of raw material used to design the machine....
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / narayanan surendran
The question did not talk about cooling and Tap Changer Type.
If over loaded, voltage drop and over heating may occur.
Therefore given rated current 263 A is correct.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sam
That depends on the rated output's power factor and the
load power factor.
Is This Answer Correct ? | 2 Yes | 3 No |
What is meant by rotor?
why do we generate only 3ph ac?is it possible to generate 4ph,5ph,....?
6 Answers Accenture, Bhel, Reliance,
sir my exam is on 19/6/2013 under electrical branch pls send me sample aptitude questions as well as sample technical questions for jindal steel and power company
what do you mean by linear and bilateral network?
what is apparent poewr, reactive power, & active power?
can we use ps class in combination with protection class in differential protection and over current protection.
what is principle of DG
the minimum clearance b/w ceiling and plane of leaf of ceilng fan shall be ..........mm
explain why core loss of a transformer is almost constant under different load conditions when connected across a constant voltage and constant frequency.
0 Answers MPPGCL Madhya Pradesh Power Generating Company Ltd,
What is IDMT? What is the principle
what happens if commutator is removed in an dc machine?
What are various power system instabilities and what are their effects on power system operation?