check list of maintenance of transformer?
Answers were Sorted based on User's Feedback
Answer / mohamed fazil
1. check cooling system of transformer and its control circuit.
2. Bushing are cleaned by soft cotton cloth.
3. Take oil sample in drain valve and send its to testing like BDV, Moisture content test,acidity test.
4. Check buchholz relay and its switches(trip switch and float switch).
5. All the terminal boxes should be cleaned.
6.Check oil leakage in transformer and rectify its.
7. Control panels (r&c, RTCC) to be cleaned.
8. Winding resistance check.
9. Insulation resistance check.
10. DGA test carried out in above 132kV transformer for 1 year and below 132kV for two years.
Is This Answer Correct ? | 1 Yes | 0 No |
Where double earthing is required? Is there any power specification to have double earthing?
purpose of flux relay for turbo generator in power plant
why the blede and jow of isoletor demage in substation?explan.
What will be the current rating of Main switch for 80 kVAR panel
How do I calculate/select Droop CT ratio for various capacity of generators?
What is the difference between Busbar Chambar, MCCB board and MCB Board? How to choose to use which one in the system?
Electronic circuit
In Transformer testing at Shop test we normally test for vector group, open ckt.,short ckt. but what are the other test performed for transformer once it reaches at site.For e.g:if the transformer is dry having rating 1000KVA?
Why magnetic flux produces an induced current?? what is the detailed procedure ?? ans plz
what is the formula for converting KW into KWH ?
Suppose an electric motor with a controller is not working. What is the sequence of testing you will do in your troubleshooting?
why the 4 terminal are named as main, line, common, voltage (M, L, C, v) of a wattmeter?? why not its nameed as A,B,C,D??