Answer / mustakul
megger is an instument which in addition to measurement of
high resistance can be used to test the quality of the
insulation at or above its operating voltage.
whereas earth tester is used to measure low earth resistance
Is This Answer Correct ? | 197 Yes | 18 No |
Answer / harish
Megger is used for measuring an insulation resistance of
motor winding of cable etc. which is measured in megaohm.
While earth tester has earth electrodes which are used to
measure eathpit resistance & it is measured in ohm.
Is This Answer Correct ? | 139 Yes | 8 No |
Answer / dolnarayan patel
Megger is used for insulation resitance measurement between
any phase and earth or ground whereas earth tester is used
to measure earth's resistance between any two points.
Is This Answer Correct ? | 66 Yes | 15 No |
megger is used to determine the value resistence of
insulation however earth tester is used to measure earth
resistence.
Is This Answer Correct ? | 34 Yes | 13 No |
Answer / jaseena
megger is used for measuring insulation resistance in mega
ohm range ,while earth tester is used for measuring the
earth resistance which is always less than 5 ohms ie a low
resistance
Is This Answer Correct ? | 30 Yes | 11 No |
Answer / sunil guru
MEGGER IS USED 2 MEASURE D INSULATION RESISTANCE OF ANY
CABLE SO THAT ANY LEAKAGE BETWEEN THE INSULATION CAN BE
KNOWN AND MEASURES IN MEGA OHM...........
AND EARTH TESTER IS USED TO MEASURE THE LOW EARTH
RESISTANCE OF BETWEEN ANY TWO POINTS WHICH IS ALWAYS LESS
AND IN OHMS.............................
Is This Answer Correct ? | 24 Yes | 6 No |
Answer / vinit patil
Basically Both are DC generators having different scales.
Megger measures insulation resistance on higher scale while
earth tester on lower.
Is This Answer Correct ? | 18 Yes | 4 No |
Answer / jai
megger is used for measuring insulation resistance between
current carrying path (when supply is isolate) to ground
while earth tester is using for measured resistance between
two points of ground.
Is This Answer Correct ? | 16 Yes | 5 No |
Answer / vkn.1980@gmail.com
megger is used for measuring insulation resistance in any
ohm range 15 tera ohms ,while earth tester is used for
measuring the
earth resistance which is always less than 10 ohms ie a low
resistance
Is This Answer Correct ? | 21 Yes | 14 No |
Single line diagram for dbb (double bus bar)system.
What are all the problems occured while ac generator running in leading power factor at full load condition?
Any website for objective type questions of electrical engineering ?
How to calculate Earth busbar size & what is the procedure we make for determine that?
Send me Model Question paper for the post Scientific Assistant in NPCIL
what is the problem in manufacturing transformer with 0 degree phase displacement.???why alwasys go for DYn11 or DY5?Whys not DY0 i.e zero degree displacement between primary and secondary side vectors?
3 Answers Bhel, dpdc, Prime Electrical,
which type of oil is used as a transformer oil?
why any centrifugal blower draw more current in starting. consider id fan and fd fan?
Differnce between negative Pahse SequenceFunction and unbalance Function?