IF avr is voltage regulator of genset means why we are
giving genset CT sense to AVR ?
Answers were Sorted based on User's Feedback
Answer / mahadevan
The voltage feedback giving to AVR for maintaining the voltage certain(nominal) limit and current feedback giving to AVR for avoid operation above certain range of current value because OLTC operation in higher current load is risky.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / gunasekaran
avr are 2 type one is voltage detection another one is load
compensation for voltage detection inout is voltage for
load compensation we have to give both voltage and current
so we r using gen avr are loadcompensation type
Is This Answer Correct ? | 1 Yes | 3 No |
Answer / leelashar kashyap
First of all, we dont have any machine that give output without input. we have CT connected to thegenset o/p &secondry of the CT is connected to the AVR. the AVR sense the current o/p of Genset & give commond to the control system of excitation to control the excitation voltage & current.
Is This Answer Correct ? | 0 Yes | 2 No |
How we can make sure cable size of LT cable without any parameter.
2 Answers Paradip Port, Siemens,
what is work of CTPT in 33/11kv Substation
Why do we use copper cable for HT Supply and why not Aluminium?
Is it weather conditions make any problems to the electrical equipments and if yes means is it any precautions needed?
IN dc capacitive reactance is??
What is the function of pulse transformer?
with 3 phase board on a 63 amp rcd is it ok to have 6 electrical showers 2 on each phase and what problems could happen
what is the difference betn earthed and unearthed cables which is commanly used why?
What is the difference between DOL starter and star delta starter
why is the power generator connected as star earthed or star earthed through reactance and what its features ?
How to calculated capacitor rating both HT
Pls say , how we calculate lux / sq.ft, which formula used for calculation