Answer / sripellirajukumar
ya ...this is rajukumar testing engineer...
As per my knowledge ...
it is very important that the secondary of a CT should never
be open-ckted,when the primary is carrying a heavy current.
this is so because
1)if the secondary is open,there is no secondary current and
no secondary flux.The large current in the primary winding
establishes a large primary flux which is unopposed,and this
not only results in huge core losses and excessive heating
of the core,but a high voltage would be induced in the
secondary, this posing a danger to the operator
2)the core gets saturated and
3)the insulation of the windings would be dameged
Is This Answer Correct ? | 65 Yes | 1 No |
Answer / max
as CT is connected in series, the if the sec side kept open
high value of the current on te primary side will saturate
the core which might be irrversible and in addition voltage
level at sec side will be very high resulting saftey issues
Is This Answer Correct ? | 22 Yes | 3 No |
Answer / max
dude as CT will step down current value it will step up the
voltage hence on the sec side resulting in very high voltage...
Is This Answer Correct ? | 25 Yes | 10 No |
Answer / k.narendra
at the primary side the no of turns is less as compared to
secondary, so if we open the secondary the secondary high
voltage at the terminals will exist because we take care
while testing the CT the secondary is closed or not if it
not the person who will at secondary will get effect of voltage
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / simon
Since the primary of a CT uses the strength of the magnetic
field around a current carry conductor to induce a current
in the secondary, it can be said the CT"S act as a source of
current. since V=IR and open circuit on the secondary cause
the resistance to approximate to infinite as a result
extremely dangerous level of voltage are induce in the
secondary, this voltage may even jump across leads. danger
may result in excessive heat causing the device to explore,
as well as electric shock of perssonel.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / ayyapss
dear Gatzrulzin ct's primary turns always less than the
sec..In pt's only the turns in the pry is higher than sec.
Is This Answer Correct ? | 4 Yes | 3 No |
Answer / ashok
First thing would be explosion of CT. Because of high
voltage generation, it will damage connected metering or
protection relays also.
Is This Answer Correct ? | 6 Yes | 5 No |
Answer / sanjay kumar
secondry winding of CT has more no.of turn with less
thickness due to this sec.winding has high voltage with low
current
if secondry winding kept open then sec.voltage will be high
and current zero
high voltage is very dangrous to a person who working near
by & keeping surrounding at high voltage
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / gourav
Transformers operate at nearly constant flux. The principle
of transformer states that in order to maintain practically
constant flux the emf induced by primary produces a current
in secondary (if loaded), which thereby opposes the cause
as per Lenz's law. If secondary is kept open, there will be
no opposition to induced emf. The situation worsens if it
is Step Up (CT) as heavy current in primary (load current)
will induce dangerously high emf across secondary leading
to saturation of core as well as hazardous situation for
working personnel.
This can also be explained by B-H curve.
Is This Answer Correct ? | 0 Yes | 0 No |
What is the maximum percentage voltage drop (vd%)for a motor control center
how to interlock 3 nos MCCBs using under voltage coil. please provide me circuit diagram?
Why a transformer is known as a static device?
what happen if transformer neutral not earth
What is the need of motor starter?
Why is transformer connect parallel? why not series? ....plz...
when the motor was star position that is running ok but when the motor was delta it was tripped? why?
5 Answers Nimbus, SEL Manufacturing,
In both 600/1000 V cable and 450/750 V cable, we can supply 415 V. However for distribution, all utilities are using only 600/100 V instead of 450/750 V. What is the reason?
How earth fault & earth leakage equvpment are works?
What current position are you holding in your current company?
Why carbon brush used in dc motor also why its not used in ac motor?
Explain Buccholz relay in detail.