What would be the ratio of a Delta-Wye tranformer having
48000 volts phase to phase on the primary and 4160 volts
phase to phase on the secondary?
Answers were Sorted based on User's Feedback
48000/(4160/1.732)=19.99
Ratio may be taken as 20.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / nain
voltage for delta side will b measured line voltage(phase
to phase)
voltage for star side will b measured phase voltage(phase
to neutral)
as u hav given both line voltages so for star side v will
convert that to phase voltge i.e.4160/1.73=2404.62
so ratio=48000/2404.62=19.96
Is This Answer Correct ? | 2 Yes | 0 No |
only three phases are coming in step down tranformers.how to get neutral?
i have a wire.and the current flowing in that.when we cut the wire then why dont we seen the elactrons....
what is G.O.D.S. ?
HOW DO I CALCULATE THE SETTINGS FOR THE DIFFERENTIAL PROTECTION OF A 12kV/6.6kV, 6MVA,DYN11 XMER WITH PRIMARY SIDE CTR 400/1 AND SEC SIDE CTR 600/1?
What is CVT and what is relation with wave trap?
What is C check in a diesel generator and what are parts and what has to be done during the C check
why use generator Earthing/Graunding.
Define early construction of human being
What are eddy current and define rms value?
What is the kva?
2 Answers Makino Auto, SAL Steel Power, Sapphire Group,
When motor stater and roter air gap do big then what will moter.
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?