WHAT AC (HI VOLTAGE TEST) VOLTAGE SHOULD APPLY FOR 33KV
CABLES.EXPLAIN IN DETAIL
Answers were Sorted based on User's Feedback
Answer / yasar
to test hipot with vlf the applied voltage must be as follows
33/1.732=19.0,this is the individual RMS phase to ground
voltage of one phase,this voltage must be multiplied three
times for three phases which gives you 57.1KV.
Is This Answer Correct ? | 5 Yes | 14 No |
Answer / ashish
For 33 KV Voltage Cable 33000*1.732 DC Volt We Have to
Apply........
Is This Answer Correct ? | 4 Yes | 15 No |