Answer / prabhu gnanasekaran
In a distribution sector your fault current sector should
be immedietly earthed in order to sequre the equipment
getting damage. So the nearest path will be provided
through out the plant.
Transformer neutral is grounded because your transformer
will be the impotant electrical equipment and this has to
be protected for fault i cannot have a neutral floating and
it has to be earthed properly. It is also earthed in order
to reduce the 3rd Harmonics effect.
Is This Answer Correct ? | 25 Yes | 9 No |
Answer / infosys
neutral grounding transformers are used to derive a
neutral-to-earth connection for systems that do not
otherwise have one.
The grounding transformer can have a zigzag winding
arrangement, or a wye-delta arrangement.
The transformer primary terminals (wye side) are connected
to the power system, and its neutral is connected to earth,
perhaps through a controlled impedance. (Usually, with
Wye-delta grounding transformers, the impedance is connected
inside the delta.) No other load is connected to the delta
of the transformer.
These transformers provide a high impedance to normal
currents (positive & negative sequence), but allow ground
fault currents (zero sequence) to flow, thereby allowing
protective devices to operate if a ground fault occurs.
Is This Answer Correct ? | 36 Yes | 22 No |
Answer / swadesh
To give output voltage a reference.By grounding nutral we
put nutral on zero potential.
Is This Answer Correct ? | 19 Yes | 6 No |
Answer / p_g
In practical cases the three phase voltages are not equal and there will be presence of potential at the neutral point and neutral is earthed to provide the path for unbalanced current during normal operation. The earthed neutral also helps during any abnormality in the system due to fault,it allows heavy currents to flow into the ground before the system isolated by means of protection system.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ashok kumar mahato(junier elec
for balancing the load on the transformer and for testing the phase at any phase of 220 or 440 volts???????not in kv,,,
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / bhaganna kolkur
When fault occurs in anyone of the phase then the fault current is increases 3 to 4 times more than the normal current so it will reduces voltage at secondry side.thise will affect the system (costly equipment) so to avoid thise neutral connection is done
Is This Answer Correct ? | 4 Yes | 7 No |
Answer / m fiaz javed
We are ground to neutral of a transformer because we give a
earth protection is opperate in any fault so we ground the
neutral of transformer.
Is This Answer Correct ? | 0 Yes | 6 No |
Answer / venkata suresh reddy
in this we can get sinsusiodal emf in 5limbed shell type and
3phase bank as well as we can supply single phase loads
Is This Answer Correct ? | 4 Yes | 18 No |
what is voltage,current,restance,. what is single phase&three phase motar. what is basic electrical 'farmoulas. what is defirens quetions of electrical maintenance.
Different STANDARDS (BS, IS, IEC etc) gives different informations on CT specification. How they correspons w r t each other (i.e I mean to say BS provides "knee point voltage" but IS does not, then how can i select CT)
what type of protection used below 132KV feeders
11 Answers APTransco, Telecommunications, wbsedcl,
Initially motor starts with star connection ,after few timing changes to delta connection, why the motor should run continously in star connection,it gives high torque & low current?
Hy the hydro power stations have high transmission and Distribution costs?
what is entropy?
Why, the starting current of 3 phase Induction Motor is 7 to 8 times its rated current?
Which generation plant has instant start
specific difference of ICT&Auto Transformer
0 Answers TNEB Tamil Nadu Electricity Board,
how to decide the rating of the ct for 1500 kva transformer
1 ton AC takes how much current( starting & stable)
If SFU is Switch Fuse Unit, What is the expansion for FSHF in Electrical Engineering?