How the real power output is controlled in a Generator?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
In case of grid connected gen ,only the prime mover can control.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / man
in grid connected alternator the active power can be
controlled by prime mover input.
if prime mover input is increased, the active power
delivered to infinite bus rises because of the increase in
load angle as E shifts away from infinite bus voltage V.
P= (E*V*sin(delta))/X
X= synchronous reactance
delta= load angle
E=excitation voltage
V= terminal voltage/ bus voltage
Is This Answer Correct ? | 1 Yes | 0 No |
what are trouble functions of transformer?ex. prv trip,oltc,oti,wti.explain detail.
kVA rating of open delta connected transformer is _____% kVA rating of delta/delta connection A 50 B 70.7 C 57.7 D 75.7
I have current, kva How can calculate kv?
In transmission line 11kv,33kv etc are rms values are peak or others??
What will be the output voltage of a transformer if it is primarily energized from a square wave voltage source?
what is the minning of propotional, integral, derivative ?
what is servo motor and how to work it.
what will happen if field winding of Synchronous generators given ac supply
what is restircted earth fault relay,how it works? what is diffrance btwn normal earth falut relay & restricted earth fault relay?
Can anybody please refer the best and simple book for about Protection relays and in detail of all its protection ?
12.5 tons a/c is their how much kva generator can recommend to the customer.
dear all, i want to ask that what is diversity factor. please explain breifly. because i hve quiet no concept about this.