IF i have switchgear with busbar current rating of 1000Amp
35kA then is it necessary to have outgoing breaker kA rating
to be equal to busbar kA rating?

Answers were Sorted based on User's Feedback



IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoi..

Answer / rajender mohan

The Busbar Rating specifies the maximum short circuit current it can see and operate, so you can put a breaker up to breaking capacity of busbar,
Ambience temprature has to taken into consideration while designing the LT Panel.

Is This Answer Correct ?    3 Yes 0 No

IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoi..

Answer / opselvaraj

Not neceesary but it is preferable to have the same rating
from operation/maintenance point of view.

Is This Answer Correct ?    4 Yes 2 No

IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoi..

Answer / anil jangra

KA rating of any switchgear is depending on fault level of connecting load,so it necessary to calculate the fault current of load than select the switchgear rating,as per my opinion the must be able to clear the fault without damaging it self and healty one feeder also.

Is This Answer Correct ?    0 Yes 0 No

IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoi..

Answer / pravin deshbhratar

yes, whatever fault current rating that we are maintaining
for the Incomer breaker same has to be maintained for
outgoing breaker also unless there is a stepdown
transformer in line. Because the fault level is calculated
on the basis of actual load of the substation that it is
going to carry out, so it is suggested that we have to use
the same KA ratiing for Incomer as well as the Outgoing
breaker.

Is This Answer Correct ?    1 Yes 4 No

IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoi..

Answer / mohammad farman khan

Not Necessary,depend upon your system means you are going
to use same KA rating for reactive power or normal power.if
you are using for reactive power then you hava to have same
KA rating of BB.however, you can check for normal load.

Is This Answer Correct ?    0 Yes 3 No

IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoi..

Answer / r.gunasekaran

Circuit breaker KA rating should be more than that bus bar
KA.

Is This Answer Correct ?    0 Yes 4 No

Post New Answer

More Electrical Engineering Interview Questions

. The string effcy in AC sys is 80% Then for same power, the string effcy in dc sys is a) less than 80% b) 80% c) more than 80% d) zero

1 Answers   Engineers India Limited,


Please send specifications for 1000KVA dry type transformer or where I can get the specifications?

2 Answers   PSU,


Please provide me detail cable voltage drop calculation

1 Answers  


Why Power generation in India is at 50Hz while in America its 60Hz so is there any advantage/Disadvantage of this ??

38 Answers   Australia Visa, College School Exams Tests, Fiat, InfoPlus, L&T, NTPC, TCS,


pls tell what are doing the three phase motor star and delta connetion with circuit diagram and control wiring .

0 Answers   Mukand,






what is pole slip ?

4 Answers   NTPC,


When will you multiply and devide with derating factors to the actual value while sizing the cable?

0 Answers  


what is the difference between Central Battery System and UPS in applications and uses? and why UPS suitable for Computers and central battery for emergency lighting?

0 Answers  


what is the principal of braker

4 Answers  


What do you mean by 4.44 in this transformer equetion E=4.44 nfqm

4 Answers   Bharat Bijlee,


WHAT IS THE FULL FORM OF CABLE TYPE-AYWY,AYWAY,YWY ?

6 Answers   Polycab, VIR, XLPE,


what is there inside an inverter and how it works?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5084)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16631)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1094)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)