Answer / nimish
there are so many reasons there may not be a residual
magnetism in d.c. generator then if critical resistance is
more than field resistance
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / j.kesavan
some times diodes failur in exciters,thats why voltage not
built in gen set
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / swayanjit
if voltage build up is not possible then there may be open
circuit in the field or armature, may be due to dirty
commutator, may be the speed less than the critical spped,
may be the field resistance greater than the critical
resistance.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / shakir
there are so many reasons:
1.the exciter might have problem
2.the ac produced in exciter is converted into dc before
supplying it to the rotor.the diodes used for this purpose
might have problem.
3.when u start the generator there should be a residual
magnetism to induse the voltage.if u will not use the
generator for long time, it will loose that residual
magnetism.for that purpose u have to give flash over
voltage.
4. the exciter winding might be grounded.
5. the input (D.C.from voltage regulator)voltage to the
exciter is not enough to create flux in the exciter.
6.faulty stator winding
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / sirisha
it is because the polarities of the field windings are
reversed.
| Is This Answer Correct ? | 4 Yes | 3 No |
How to protect a Dosing pumps/any sensitive equipment (single phase) from surge protection inside a food factory.
What is GNR ? How much value of ground neutral resistance?
why there is a high voltage line in multiplication of 11?i.e.- -66kv,11,kv,22kv
how to find three phase complex power in per unit and MVA?
Why single phase induction motors are not self starting ?
what is formula in determining the size of Circuit Breaker for transformer with the following specifications. 7 units of 1600 volts (primary) and 400 volts (secondary). Both Primary and Secondary will have a circuit breaker which is SF6. What should be the Switchgear Main Breaker Size anf the sizes of each brances Circuit Breaker for Primary.
how to calculate power consumption in slip ring motor at different step
i need 24v dc from 230v ac supply how we can getit ? what are the devices &its rating requied for that ? plzz i need answer urgently .thank u
what is the differance between MC61C and MC61A relay of L &T make.
Why rating of transmission line in kv not in kva
Why do series motors have high starting torque?
what happens when dc supply is given to the transformer?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)