In a Circuit how the MCB and Fuse ratings are calculated.
And shall the fuse follws the MCB or it is otherwise?
Answers were Sorted based on User's Feedback
Answer / sanjay kumar
FUSE RATING CAN BE CALCULATED AS FOLLOWS:
SAY A MOTOR FULL LOAD CURRENT RATING IS 30A,TAKE FUSE OF
RATING 2.5TIMES OF FLC. SO FUSE RATING WILL BE 80A.IF IN
CASE THIS RATING FUSE IS NOT AVAILABLE, WE CAN GO FOR NEXT
HIGHER LEVEL. BUT IF NEXT HIGHER LEVEL FUSE IS SO HIGH THAT
IT CANT BE TAKE THEN GO FOR SOMEWHAT LOWER LEVEL. THIS IS
BASED ON MY EXPERIENCE IN THE INDUSTRY.
SECOND PAART IS FOR MCB:
MCB SELECTION SHOULD BE SOMEWHAT HIGHER THAN FUSE RATING.
| Is This Answer Correct ? | 5 Yes | 4 No |
Answer / amaravathi
fuse rating will be calculated by following formula.
125% of rated current.but we can use nearest value of fuse rating value.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / devamanohar
The MCB rating shall be more than the fuse rating if it is
used for the service to switch off & on while the circuit
is in service.The fuse rating shall be 200% of the rated
curent normally as it is used for short circuit
protection.If the MCB is stay put type(No operation while
in service) it can be selected for rated current or 1.2
times of rated current value.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / shaik
depending on the full load capacity ratings is calculated.
It is not necessary to connect MCB and fuse both,one is
enough.if u want to connect both then first fuse the MCB
| Is This Answer Correct ? | 11 Yes | 15 No |
Answer / mahesh s.chorghe
MCB RATING SHOULD BE 2.5 TIMES OF LOAD CURRENT AND FUSE
RATING GRETER THAN (1.5 TIMES)MCB
| Is This Answer Correct ? | 14 Yes | 29 No |
Answer / moideen.t.y
Fuse size can be calculated by this formula, 225% of full
load current.
locked rotor amps is the 500% of full load current.
| Is This Answer Correct ? | 4 Yes | 19 No |
what do you mean by type zero control sytem ?Give an practical example of type zero contol sytem?
what will happen, if both relay contact has live supply, and coil of relay activated
What happens to the terminal voltage of an alternator connected to a bus bar when it is suddenly disconnected from the bus bar??
What is creepage distance..... what will be the value for different voltage level
Our Slip Ring Induction Motor Frequently tripped By Earth Fault While Starting time and in Normal Operation Time also Kindly Let me Know the Reason. Application Ball Mill - Cement Mill
Whether IP65 enclosure box blocks ventilation if driver for LED have to enclosed inside IP65 box
what is the transformer
is there any current flows in our body?
what is full wave bridge?
how the synchronizing is obtained at bus couplers in grid substation? (because there we cannot change the frequency in one of transmission lines like in generator synchronization)
why we are using Load factor?
can we use 220 volt 15 w a.c. lamp on 220 volt d.c.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)