Answer / gans

kVA is the unit for apparent power. Apparent power consists
of active and reactive power. Active power is the share of
the apparent power which transmits energy from the source
(generator) to the user. Reactive power is the share of the
apparent power which represents a useless oscillation of
energy from the source to the user and back again. It occurs
when on account of some »inertia« in the system there is a
phase shift between voltage and current. This means that the
current does not change polarity synchronous with the
voltage. But the heat generated in a winding as well as the
eddy current losses generated in a transformer core depend
on the current only, regardless of whether it aligns with
the voltage or not. Therefore the heat is always
proportional to the square of the current amplitude,
irrespective of the phase angle (the shift between voltage
and current). So a transformer has to be rated (and
selected) by apparent power.

Is This Answer Correct ?    0 Yes 0 No

Why Transformer in KVA?..

Answer / hazari sharma

primary and secondary voltage are rated on accont of rated current flowing both winding that,why cu losses which depands on current and iron loss which depands on voltage and easily calculate that'swhy t\f rating done in kva.

Is This Answer Correct ?    0 Yes 0 No

Why Transformer in KVA?..

Answer / sumesh raut

As we know that the cu loss of depends upon current and iron
loss depends upon voltage so total loss of transformer
depends upon voltage and current i.e(VI)or (KVA) and doesnot
depends upon angle between them i.e(cos(phi)).So the rating
of transformer is in (KVA).

Is This Answer Correct ?    0 Yes 0 No

Why Transformer in KVA?..

Answer / rockyxyz

the only answer to this question is that the power factor
of load is not known while designing (it is leading or
lagging) so transformers are rated in kVA. The required
size of X-mer depends on the power factor of load connected
to it.

Is This Answer Correct ?    0 Yes 0 No

Why Transformer in KVA?..

Answer / prabas

transformer rating only in KVA because copper losses depends
upon current(I^2R) and iron losses depends upon voltage.
iron losses are 2 types 1)eddy current losses 2)hysterises
losses so total losses depends upon I,V not on phase angle
between i and v.so t/f rating always in KVA not in KW.

Is This Answer Correct ?    0 Yes 0 No

Why Transformer in KVA?..

Answer / manikandan

Copper loss depands on current and Iron loss depands upon
the voltage.hence the total loss depands upon only VA. not
a phase angle between voltage and current . ie it is
independant of load power factor .Thats why rating of
transformer given in KVA and not in KW. It may be further
point out that temp. rise of the transformer is directly
proportional to apparent power which flow thought it.

Is This Answer Correct ?    0 Yes 0 No

Why Transformer in KVA?..

Answer / dipak sonkusare

Transformer is a static machine. As there are two types of
losses - Cu loss and Core loss. Cu loss depends on current
where as core loss depends on voltage and power factor does
not matters. Also the connecting load is unknown where it
will supply the power i.e., it may be inductive /
capacitive / resistive load. Hence the transformer rating
indicated in KVA instead of KW.

Is This Answer Correct ?    0 Yes 0 No

Why Transformer in KVA?..

Answer / vamsidhar

copper loss depends on current(amp) and iron loss depend on
voltage(volt) ,hence transformer rating is in kva

Is This Answer Correct ?    0 Yes 1 No

Why Transformer in KVA?..

Answer / ss

rating of any machine depends on temparature rise of the
machine ,temparature rise depends on losses in the machine
,in t/f losses r independent of power factor they depends on
voltage and current,but in the case of other machine losses
depends on pf

Is This Answer Correct ?    0 Yes 1 No

Why Transformer in KVA?..

Answer / rajesh

we know
output=Input-Losess. 1

and the losess in transformer are two types ohmic, core
losess and these are depends on the Voltage and secondary
current , independent of P.F.

so the rating of losess is in VI not VICOSPIE.From equation
1 losess in KVA so rating of T.F also in KVA.

Eg.if any machine connected at noload, the output put is
zero, because of no current from below equation.
VICOSPIE.

But in T.F there will be some power cosumption inform of
loss.i.e. core loss.

Is This Answer Correct ?    1 Yes 4 No

Post New Answer

More Electrical Engineering Interview Questions

kVA rating of ordinary transformer is increased when connected as an auto transformer because A transformation ratio increased B secondary voltage increased C energy is transferred both inductively and conductively D secondary current increased

0 Answers  


What is the principal of motor?

0 Answers  


from generating station If 400v LT line length is 1000m how much voltage is drop and how do i calculate it? which cable will be use for this line?

0 Answers  


what are the disadvantages in GIS over AIS

0 Answers   Tata Steel Limited,


if the 10 hp motor name plate indicates rated current as 13.6 amp the what will be the thermal relay setting? Why? And in how much time relay will trip at the set value?

2 Answers  






why transformer cannot rotate though the princplebehind induction motor is similar to a transformer?

2 Answers   GE,


IT IS DESIRABLE THAT THE INCOMING MACHINE SHOULD BE A LITTLE FAST AT THE TIME OF SYNCHRONIZING.EXPLAIN?

1 Answers  


what is the MF if CT ratio is 500/5 and in meter specification is 3.75 REVS/KWH? Thanks and Regards Selvendran.N

1 Answers  


One VFD is possible to connect two motors at the same time?

2 Answers  


How reverse power relay sense the power is reverse in the system.

2 Answers  


Dear All, Pls let me know about ELR.... CBCT is using for singnal purpose... How it works.. any body can explain pls.......

4 Answers  


why should the lowest unit of a testing transformer ( cascaded transformer ) have higher power rating??

0 Answers   TCS,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)