in our 6.6kv motor feeder[it is having two sources from
Bus A&B] earth fault relay is acting, we checked CBCT
connection and cable meggerd values found very good still
earth fault acting during first two are three start after
that it will hold. please clarify what was the reason. if
same motor is starting from other Bus-A it will start.
WHAT IS THE TYPE OF 6.6KV SW.GR. hOW OLD IS THIS?
tHE EARTH FAULT RELAYS ARE VERY SENSITIVE. INSULATION
RESISTANCE OR MEGGER CAN NOT MEASURE.
CARRY OUT HV CAPACITANCE MEASUREMENT OF MOTOR,CABLE FEEDER.
AND hIGH POT TEST.
MEASURE THE TANGENT DELTA FROM DC HIGH POT.
IF MIN OIL CIRCUIT BREAKER,TEST THE OIL AND REPLACE.
WE ALSO EXPERIENCED THIS DUE TO BURNED CEREMIC/BAKELITE
PARTITION PLATES OF 6.6KV SW.GR
Is This Answer Correct ? | 0 Yes | 1 No |
what is the difference between main meter CT and check meter CT?and what is the difference between main meter PT and check meter PT?
what is the purpose that we use PLC system in power system
what are the types of transformers
what is the working principle of electrical generator
howmany electrician should maintain for a 1000 kva used plant... in kerala..
Dear All, Pls let me know about ELR.... CBCT is using for singnal purpose... How it works.. any body can explain pls.......
what is the different between RCCB & ELCB
Dear all, kindly give me the details of leectrical design engineer course details/institute in hyderabad /any where in india.
What is Avg. Power Consumption of 2 TR Split A/C???How v can calc. this???
can we start mulitple 3 phase induction motors with common starter?
how to calculate the neautral earthing conductor size for a 500kva dg set.
1.what is electricity 2.what is electronice 3.how many modules 4.five electrical component with symbol 5.five electronice componene with symbol 6.how convert 220v.A/C to 24v/DC 7.220V.WAIRING DIAGRAM OF AMMETER/VOLTMETER/OHMMETEER