WHAT ARE THE FACTORS REQUIRED FOR SELECTION OF TRANSFORMER
RATING?
Answers were Sorted based on User's Feedback
Answer / kannan.sj
first u should know
1,The connected load of transformer or load factor
2,Highest connected load / motor in the transformer and its
starting type
3, diversity factor
because
KVA demand at 0.8 p.f =connected load x LF x DF
-------------
efficiency X p.f
starting current of highest KW load takes 6 times of full
load current. so we to check it whether the transformer has
the capability to feed the load or not during starting. its
the important thing while considering trafo selection..
| Is This Answer Correct ? | 57 Yes | 6 No |
Answer / guest
You need to know the load type and calcuation of schort
circuit
| Is This Answer Correct ? | 25 Yes | 14 No |
Answer / ahfaz
1] we have to know the KVA load required
2] we have to know the percentage of impedance in the winding
3] Indoor or Outdoor
4] Type of cooling
5] Maximum temperature required
Thanks & regards
Ahfaz
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / shaista
SECONDARY LOAD VOLTAGE
KVA Rating
application of use
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / mohammed hussain a
Load Current,Load Voltage and Load Power factor(Secondary
Side). It may 3 Phase or 1Phase.
For 3phase Power in KVA = 1.732*V*I/0.8*1000
For 1 Phase in KVA = V*I/1000.
The rating of the transformer can be identified from the
above formula.
| Is This Answer Correct ? | 13 Yes | 11 No |
Answer / mgm
calculate all connected load like lighting load power load
motors ahu etc, calculate the 3 phase current and multiply
it with 1.25%
we will get the transformer size
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / manasa
First we have to know about the load consumption, then
diversity factor that is demand in KW and then in KVA
| Is This Answer Correct ? | 7 Yes | 10 No |
What is the distance between body earthing and neutral earthing.?
how do i commission a distribution transformer knowing all its ratings and transformation ratios?d
If any one's require of phoenix contact like( relay , termilnal block , surge protection device ) , product please contect me 09878206357 chetan verma
calculate multiplication factor of a trivector meter with line ct ratio 200/5A, line PT ratio 11000/110V and meter CT ratio 200/1A and meter pt Ratio 11000/110V.
if 40 watt bulb has higher resistance then a 100watt bulb then according to joul farmula p=I^2R the 40 watt bulb more power consume then 100 watt bulb.
Why ct secondary is not kept open while primary charged. Answer in terms of ct parameters.
What will happen if we do not provide earthing to the newtral of a power system ?
what is linear elements
What is LCI drive & how does it work & why it is used?
How to select batteries required for ups and the inverter if we Known load? And how AH is selected of battery?
Application wise, where we should use AC motors and where we should DC motors?
i am BSEE student, my project study is to synchronize the generator of an hospital, it have a one 313KVA standby-power diesel gen.,and three 100kva transformer.The generator system is operated manually and no ATS or UPS. one more new building is being build so the transformer will be upgrade to a higher vale. 1)how i can connect the new gen. to the old gen. and to the synchronize panel? 2)what is the new gen. to be buy?(rating, etc.) These is my title: To synchronize the generator system of the ____ Hospital. Anyone have a good title? Thanks.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)