how to find motor contactor rating and bimetalic relay
rating? of 30kw motor which will operate on star-delta
starter?
Answers were Sorted based on User's Feedback
Answer / elangovan t
You can use Type2 coordination table to find out the
contactor rating and OLR rating.
Normally the OLR should be set at the Full load current
rating of the motor. Hence the OLR may be selected such that
the motor flc lie in the mid range of the relay span
| Is This Answer Correct ? | 17 Yes | 2 No |
Answer / ashish
FOR 30 KW MOTOR CONTACTOR RATING IS AS PER KW MENS 1 KW FOR
1 AMP CONTACTOR FOR SD STARTER FOR 30 KW MOTOR 30 AMP
CONTACTOR AND RELAY SET ON MOTOR FULL LOAD AMP. MULTIPLY BY
(.64).
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / aksx
how to find relay range and relay setting of three phase induction motor of 30kw ratting.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / thakur
Full Load Current of Motor-52Ampas per(415.1.732.0.8)
Usually we are using any protective divece/conducter 1.5
time of higher side.then Contactor Carrying Capacity Will
be-80amp and Over Load relay Capaciry wil be-80 Amp and its
over load setting will be-30 amp as per (LI/1.732)
| Is This Answer Correct ? | 10 Yes | 13 No |
Answer / abhijit
as 30kw is rating flc=52 bmr relay setting will be 50 as it
should be slightly less than flc,contactor should be more
than flc but it depends upon the application coupling
| Is This Answer Correct ? | 1 Yes | 4 No |
Answer / sanjay
40 hp motor full load current appx 52amps so we have use
2.5 times relay rating and power contactor rating.
| Is This Answer Correct ? | 9 Yes | 26 No |
Is it possible to use AC supply insted of DC supply in trip coil operation? if not, why?
how to synchronize 4 nos. of diesel generator sets of different capacity (kva)?
How i can calculate current of cable according to ares?
why CERAMIC material is used in insulators??
what is the condition for vector group of Dyn5
what is the working difference b/w softstarter and Variable frequency drive ?
how calculate the current faut level
how to calculate 'In'in a system?
why motor burns ?
how to calculate fuse rating for a motor
What is the difference between Droop vs Isoch Control?
How to work E.L.C.B and how to connect in circuit.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)