Is voltage & potential transformer are the same? Are they
used for same application ?
Answers were Sorted based on User's Feedback
Yes VT and PT are same.
it is mainly used for Protection and metering.
the Tx.line have high voltage. if you want to measure the
voltage it should also designed with HV. it leads more cost.
therfore we are steping down the voltage to a low level. it
is usally 110V.
also it is used for distance protection. the distance
protection is based on Impedance. Impedance can be
calculated by using the formula Z= Voltage/Current.
Is This Answer Correct ? | 19 Yes | 3 No |
Answer / shobana
Yes both are same. They are used to measure the voltage in
the electric circuits. Their main role is to condition
(step down) the voltage to be measured to levels suitable
for the measuring instrument.
Is This Answer Correct ? | 19 Yes | 6 No |
Answer / abhishek kanojia
Yes Potential and Voltage transformer are same and their
use are not only resticted to measuring purpose only but it
is further supplied to relaying panel or to trip circuit so
that the protection purpose and measuring are
simultaneously get satisfied accordingly.
Is This Answer Correct ? | 13 Yes | 4 No |
Answer / sewagudde
VT and PT are the same thing. they step down high voltages
(132kV,33kv, 11kV etc) to a nominal value usually 110v
which is used to energize substation instruments such as
protective relays.importance of this is not to have bulky
relays which can withstand high voltages.
Is This Answer Correct ? | 7 Yes | 3 No |
Answer / sohail
yes. There are 2 uses of pt/vt.
First they can be used for measuring purpose of high rating
voltages through step down.
Its other use is for protection purpose for protecting
generators,transformers.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / minal
Yes both r same. They r used to step down the high voltages
to a lower voltages that can be measured by instruments
like ammeter, voltmeter,wattmeter & relays which r used for
protective purposes.
Is This Answer Correct ? | 5 Yes | 3 No |
Answer / chethan
NO,They are different VT(Voltage Traf.) is used to step up
& step down the voltage perpose
PT. is used for Protection of equipment & measure the
voltage
Is This Answer Correct ? | 3 Yes | 3 No |
Answer / vels
yes friend
PTs are connected in Bus side or Line side
used for metering and
protection for Distance relays ,directional overcurrent relays ,under/over frequency relays ,under/over voltage relays ,synchronising Gens and Lines
open delta measurements
line healthy etc
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kruvesh sharma
yes it is same but cant use for same application
Is This Answer Correct ? | 2 Yes | 6 No |
Answer / r r estake
vt's are voltage transformers, based on inductive
principle,pt's are potential transformer's and covers vt &
cvt (capacitive voltage transformers).applications are same
but working is different.
Is This Answer Correct ? | 1 Yes | 11 No |
what is the difference between electrical & electronics
245 Answers Axon Constructions, Banking, GDA Technologies, Infosys, MBA, Satyam, Satyam Tech, Snow White, TCS,
What is the method of Tan delta test for power Transformes and why it is required.
how many by pass system in online UPS.
how to select the surge suppresor for the 33 KV supply and what will be the rating, selection guide
What are the neccessary safety arrangements before commissioning of HV substation?
why rotor current reading is taken & why not stator?
A 400 V, 50 Hz, Δ connected synchronous generator has a field reactance of 0.1 Ω and armature resistance of 0.015 Ω. At full load, the machine supplies 1200 A at 0.8 pf lagging. Under full-load conditions, the friction and windage losses are 40 KW and the core losses are 30 KW. What is the machine’s overall efficiency? Ignore any field circuit losses.
what is the working principle of contactor and conditions of normal open and normal close on it?
is it possible to say motor horsepower number without seeing name plate(when name plate damaged)
If a air condition consume 2.50 to 3.00 amp then how much it will consume in watts if it is running 10 hours out of 24 hours????
why we used star delta starter for above 5hp motors
I have 3 1000 kva single phase transformers and I wish to replace them with one three phase transformer. What is he kva rating of the new three phase, is it 1000 kva also or 3000 kva.