Can we use mov instead of esdv Explain the reason
Answer / elham
Hi
No we must not use MOV instead of ESDV. As you know MOV's are working with power but ESDV's are working with Instrument Air (closing and opening) so in the case of power outage we can't close or open MOV but in the case of IA outage we can adjust ESDV on fail safe mode. so ESDV's that should work on emergency cases always are reliable with IA.
Is This Answer Correct ? | 0 Yes | 0 No |
Why are the uses 24vdc in industries
What is use of condensate pot
5 Answers Alstom, Petrocil, Samsung,
how to define the P,I,D value in tuning pid loops in online.
Give Detail information about plc,dcs,and scada system?
what is the difference between Cv and air consumption? why the customer needs Air consumption details?
i have used level transmitter in starch cooking preparation tank. tank total height 2mtr.sometime LT display shows some error value when tank is fully empty and diaphragm side i already checked okay no problem in diaphragm area. field cable checked 24volt and mA shows correct value while tank empty mA is 4mA. 4mA i needed that 0% but display showing 10% or 15% percentage values are varying continously please give any good solution for me.....
different between calibration range and instrument range ?
what's the criteria of using over range protector when installing Pressure Gauge
How to change dcs card in online. (Dsc is maxdna)
How many loops are there in the power plant? how many closed & open loop in the power plant ? Please give me the exact clarification?
why we are using drum level control valve air to close?
If a warning lamp will operate with the ground circuit is bypassed with a jumper wire to ground, what should you check?