How Control valve sizing is done?
Answers were Sorted based on User's Feedback
Answer / e mohana priya
A basic liquid sizing eqtn.. is as follows:
Q = C
V
∆P / G
(1)
where:
Q
=
Capacity in gallons per minute
C
v
=
Valve sizing coefficient determined experimentally for
each style and size of valve, using water at standard
conditions as the test fluid
∆
P
=
Pressure differential in psi
G
=
Specific gravity of fluid (water at 60°F = 1.0000)
Thus, C
v
is numerically equal to the number of U.S. gallons of water at 60°F that will flow through the valve in one minute when
the pressure differential across the valve is one pound per square
inch. C
v
varies with both size and style of valve, but provides an
index for comparing liquid capacities of different valves under a
standard set of conditions.
To calculate the expected C
v
for a valve controlling water or other
liquids that behave like water, the basic liquid sizing equation
above can be re-written as follows
C
V
= Q
G
∆P
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / abdulbasit137@hotmail.com
control v/v depend to pv bcz pv i mean process variable
flow.flow types laminar,turbulense .transational, & flow
which gas flow, fluid flow,. another we done the cv size
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / ganpat002
Cv=q/[[change in pressure/specific gravity]^0.5]
| Is This Answer Correct ? | 3 Yes | 9 No |
what is buoyancy law?
what does 5/2 solinoid valve means?
What you mean by multi stage control vavles?
what is temperature compensation?
If the Barrier Fails during online then What will be the control valve position in field or Positioner action in the field.
Which type of diaphragm use in costic line, dm water line, natural gas line, oil line?
I am a electronics and instrumentation fresher trying for a job in IT sector. what do need to prepare for the interview?
What is PDS and PDMS ?
what is the difference between mmhg & mmwc?. i want to calibrate a transmitter in the range of -100 to 300 mmwc. Which is the reference for calibrate the Tx,if mmwc not available?. Is it mmhg or mmho2?.
why ultra sonic level transmitter is installed in 90 degree?
Calibration procedure for electro magnetic flow meter
i have used level transmitter in starch cooking preparation tank. tank total height 2mtr.sometime LT display shows some error value when tank is fully empty and diaphragm side i already checked okay no problem in diaphragm area. field cable checked 24volt and mA shows correct value while tank empty mA is 4mA. 4mA i needed that 0% but display showing 10% or 15% percentage values are varying continously please give any good solution for me.....
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)