why to use 3 wire at RTD ?
what's the reason for
common wire ?

Answers were Sorted based on User's Feedback



why to use 3 wire at RTD ? what's the reason for common wire ?..

Answer / prince

RTD's work on the principle of RESISTANCE. The two working
wires might have different lengths, so different resistance.
Third wire is used for compensating the extra resistance so as
to get accurate o/p. Third wire is in parallel connection with
one of the wire. In 4 wire RTD, the compensation is more.

Is This Answer Correct ?    13 Yes 0 No

why to use 3 wire at RTD ? what's the reason for common wire ?..

Answer / carl_ellis

It is correct that an RTD indicates a change in temperature
by a change in resistance of an element.

The change in resistance must be monitored electronically
and any circuit connected to an RTD will include copper lead
wires which will add resistance to the circuit.

The problem is not that the lead wires will have different
lengths, the problem is that any copper lead wire has some
resistance which will contribute to a voltage drop from the
source current and appear to be the resistance of the RTD
element. Any contribution of resistance to the measurement
is an error.

Two lead wires connect to the RTD element and a 3rd lead
wire is used to compensate for the added lead wire
resistance so that the lead wire resistance is eliminated
and only the RTD resistance is measured and used to
calculate temperature.

Carl Ellis
Measure First

Is This Answer Correct ?    10 Yes 1 No

why to use 3 wire at RTD ? what's the reason for common wire ?..

Answer / rathod mukesh r

If 2 Wire rtd use , The distance is more between remote location (Rtd) And dcs panle then error occur in reading of temperature. Means if wire length is increases then its own resistance also increase so proper reading is not transmited via 2 Wire. In 3 Wire rtd these error is remove using compensasion lead.

Is This Answer Correct ?    0 Yes 0 No

why to use 3 wire at RTD ? what's the reason for common wire ?..

Answer / yugesh shah

3rd wire is called compensation wire , when RTD is installed
far away from control room or where we get indication then 2
wire RTD fails to send appropriate sign al due to
temperature effect or atmospheric changes so 3rd wire is
helpful to send error free signals or resistance

Is This Answer Correct ?    0 Yes 2 No

Post New Answer

More Instrumentation Interview Questions

why we use cascade control and feed forward control in 3 element drum level control measurement of steam drum .what is cascade and feed forward control system ?give example .

0 Answers   Visa Steel,


The process variables that need to monitored and controlled are ________, ________, _________ and

1 Answers  


If relative y axis vibration sensor is by passed, and relative x axis and absolute sensor is left working. how much monitoring i would have risked?

0 Answers  


What you mean by multi stage control vavles?

0 Answers  


TECHNICAL/ARTITUDE

0 Answers   ONGC,






hi my name is rakesh patel i just complited my be in instrumentation & control now i am going to working as a validation engineer in a poject department so what is a scope in a future as a validation engginer ? what line is good for me can any bady give me complete solution please? your regard rakesh patel

0 Answers  


A motor is taking 15 Amps at no load and 60 Amps at full load. and a valve has to open 10% at full load and 80% at no load. How to draw ladder logic.(PLC).

2 Answers  


What is the potential contact / output??

1 Answers   Vasava Engineering Private Limited,


what is the difference between cold loop and hot loop

2 Answers  


dear friends, i have seen flow as the selection critriea in presure guage (bourdon tube) and i would like to know what is the relation between flow and performance of pressure guage other parameters i found in the data sheet are pressure max. 1ksc temperature max. - 50 deg c line size - 80NB operating range - 1ksc pr. guage range - 0-2 ksc thank u,

0 Answers  


What is the working principle of sox, nox analyzer?(opacity monitor) Otherwise how to measure the sox,nox?

1 Answers   Thermax,


What is Electrical Runout & Mechanical Runout in Vibration measurement.

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)