Answer / subash krishnan
Instruments required:
Multimeter, potentiometer, point position trnasmitter (PPT), Valve Positioner, allen keys 3mm and 4 mm , double-end spanner (12-13), mini screw driver.
1.Initially check the motor-operated valve for open/close manually since the torque set should be accurate inorder for accurate calibration process.
2. Choose a potentiometer a desired based on the number of rounds in which the valve opens or closes. For example if the rounds are maximum choose a potentiometer which has the lowest resitance (1 kilo ohm).
3. Also choose the matching teeth wheel for the chosen potentiometer.
4. Take a point position transmitter (PPT) which is used to give the present position of the motor-operated valve. The PPT is of two different ranges based on resistance (0 to 230 ohms) & (0 to 500 ohms)
5. For every motor-operated valve the close position resistance is set as 100 ohms and the open position is set as 230 (to 500 ohms).
6. The point position transmitter is now given the power supply of 24V DC .
7. Now the resitance for the close position i.e. 100 ohms is given as input and the current should be tuned as 4mA.
8. Now the resitance for the open position i.e. 230 to 500 ohms is given as input and the current should be tuned as 20mA.
9. The steps 7 & 8 are repeated until the PPT gets set to 4 to 20mA.
10.Now the teeth wheel is matched with the matching wheel in the motor-operated valve setup so that the resistance could change in accordance with the valve's open/close operation.
11. The valve is now checked for open/close so that the current for open/close should be in the range of 4-20mA.
12. Now the positoner unit should checked whether it displays 0-100% for the open/close position. Otherwise the positioner display should be tuned for 0-100%
13. There is an actuator tuning adjustment in the positioner unit inorder to do fine calibration for zero and span if there are any minor errors in open/close position.
| Is This Answer Correct ? | 10 Yes | 0 No |
Is Hart communicator calibration device or communicating device for transmitter?
how can i check vortex shedder bar it is ok? if there is ohms condition are shown correct?
Tell me the field calibration procedure step by step with diagram of temperature transmitter, temperature indicator, flow indicator, level indicator, control valve, thermocouple, pressure indicator (digital & analogue).
what is positive displacement meter.
Explain about SOURCING & SINKING concepts in PLC to field sensor wiring ?
How will you test a transistor with a multimeter?
I have 475 hart communicator. this is not support any new type of instruments such as tranmitter,fieldvue DVC6200.DVC 200 since i got point out need to upgrade . my questions is how can upgrade new instruments software in my 475 hart communicator. can any answerplease>?
difference between dcs & pld
i have done DAE in Instrumentation and Process Control. i have applied for an apprentice training in chemical company after three day my interview will be conduct but i need more information about industrial process control and controller. my e mail is imran_dilsetu@yahoo.com please tell me interview question relative to instrumentation ?
what does ip65 signify??what is its NEMA equivalent???
What is difference between radial vibration and axial vibration explain in detail .
what is the differnce betweeen hart and smart tx
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)