my project load is 6 MW so please suggest the size of cable.. ALU 3c 400 aqmm cable can be sufficient.. is there any thumb rule for calculation of cable size please help me
Yes there's a thumb rule for cable size calculation for 1sqmm Aluminum cable can carry 2Amps and 1 Sqmm Copper wire can carry 4 Amps.
However the cable size increase above 100 Sqmm this thumb rule can not be considered. You need to refer the cable size calculation chart.
Is This Answer Correct ? | 0 Yes | 0 No |