How we find the size of cable if we know the current
Answers were Sorted based on User's Feedback
Answer / aju
We can choose the cable according to the current rating
after considering overload and voltage drop factors
Usually cables are loaded upto 75-80 % of the rating
specified by manufacturer ..
For instance, if you need to choose a cable for a current
rating of 25 A, we can simply choose 6 sq.mm cable since it
can carry 35 Amps. It is desirable not to use 4 sq.mm cable
which has a current rating of 28 A since it has no
sufficient spare capacity for overload condition.
Again, the cable size also depends upon the voltage drop
which depends upon the length of the cable....
usually voltage drop must be within 3-5 % range.If it
exceeds this limit then next higher size must be used until
it satisfies the 3% range
Eg. for calculation of voltage drop in 25A, 240V single
phase feeder having 150M length
Voltage drop/Ampere/Metre for 35 Sq.mm cable=2.1mV
Voltage drop= (2.1x25x150)/1000 =7.88V
% Voltage drop= (7.88x100)/240 = 3028%
Since it exceeds the 3% range, take next cable size
Voltage drop of 50Sq.mm cable= (1.6x25x150)/1000 =6V
% Voltage drop =(6x100)/240 =2.5%
Hence, we can select 50Sq.mm cable
| Is This Answer Correct ? | 74 Yes | 15 No |
cable size can be selected like ,suppose if u have any
motor with u of 110kw and its full load current is 190 then
when it is in dol stater starting torque is high up to 2
times of that full load so we have to use 300sq mm.if it is
in star delta 240 sq mm is enough because in a star
starting current is low it means 70 to 60 percent of full
load .after that some time delay delta pick ups
| Is This Answer Correct ? | 40 Yes | 21 No |
after how many spot we must chang secondry cable in portable spot welding gun?
Define what is the function of anti-pumping in circuit breaker?
Alternator couple to diesel engine why, Alternator couple to ac service motor with gear drive for 1500 rpm possible (yes or no) aim to low input power supply give to motor then high output power taken for alternator Please answer this question
acb(AIR CIRCUIT BREAKER)NOT CHARGING AUTO
In Round type three phase transformer why the LV side is inner part and HV outer part in the design of transformer? why they cant be opposite?
why neutral and earth should not be connected on 3 phase 440v/50c/s supply at consumer side. where as on 25kv/ac/50c/s railway traction substation neutral and earth will be connected and track at substation. and track will act as neutral and earth. Reasons for this is needed urgently
What is the main feature of v/f control?
what is multiplying factor of a energy meter connected with a CT ratio of 600/5 and voltage at 415 volts.
Is there any design in the world a 220 KV transformer without breather …??????
what is the d/f b/w iverter & converter.
I HAVE A 50A MCCB AS PER DESIGN LINE WIRE CONNECT UPWORD SIDE AND LOAD IS CONNECTED TO DOWNWARD SIDE TO THE MCCB.IF NOW ANY ONE CHANGE SUPPLY & LOAD(WISEVERSA) WHAT HAPPENS ? DOES MCCB OPERATION OR WORKING FUNCTION NORMAL IF YES THAN WHY THERE ARE MARKED LINE & LOAD ON MCCB.
What meant by lagging and leading? When if they are occurred what preventive methods should be taken?
14 Answers ABB, L&T,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)