if found error in magnetic flow meter?how can we adjust?
Answers were Sorted based on User's Feedback
Answer / kumaran
1.The magnetic flow meter should not shows the error if it is properly grounded and properly terminated with transmitter.
2.Always the installation should be made like valves before and after the sensors. while showing error in the meter, you should close the downstream and upstream valves to check the zero. If it is shows zero then there is no error in the zero point.
3.Check the span error by weihging the flow. the sensor output pipeline should be connected to the tank and measure the tank area, fill the tank and check the span between tank capacity and the flow rate.
4.make sure that the observing coils inside the sensors are clean. else try to clean the same.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / cbell
short circuit the two electrode (E1 and E2) in the terminal and adjust the zero (4 ma)
| Is This Answer Correct ? | 0 Yes | 0 No |
Absolute pressure is 700psi,what will be the gauge pressure?
Yokogawa dcs normally where will change 4-20 MA to DC voltage( node or I/o cards?)
HOW TO CALIBRATE A PRESSURE SWITCH?
can you send remote seal interface level transmitter calculation steps for oil water saperator.
0 Answers Sasol Firm, Thermax,
in a electronic controller why we are using 250 ohm resistance in input signal?is i/p is necessary in control valve when we are using electronic controller give details?
How many loops are there in the power plant? how many closed & open loop in the power plant ? Please give me the exact clarification?
what is an ambient temperature?
why we use 250 ohms across HART CALIBRATOR DURING CALIBRATION OF TRANSMITTER
How to find out turn down ratio of Pressure transmitter?
How to calibrate displacer type level transmitter (chemtrol make )for level measurement in hotwell , LP & HP heater ?
Sir,I am going to sit for IOCL written test exam. recently.Can anyone tell me the name of 'Objective type Question Book on Instrumentation Engineering ' which will help me. Pl. mail to bidyut_71@rediffmail.com / bidyut.saha2008@indiatimes.com / bidyut.saha09@yahoo.in
What are de-saturators?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)