in a electronic controller why we are using 250 ohm
resistance in input signal?is i/p is necessary in control
valve when we are using electronic controller give details?
Answers were Sorted based on User's Feedback
The hardware electronic controller you are using has a 1-5
Volt input but the transmitter you use in the field, is a 4
to 20 mA transmitter. So in order for the hardware
controller to accept this input, you install a 250 Ohm
resistor on the controller's input which will convert it to
a 4 to 20mA input.
Weather you need a I/P converter on the control valve
depends on the positioner you will use. The hardware
electronic controller will give a 4 to 20mA signal to the
control valve, so if you want to use a full pneumatic
positioner on the valve, you need to install a I/P converter
and calibrate it for a 4 to 20mA input and a 20 to 100 Kpa
pressure output. You then need to calibrate the pneumatic
positioner for a 20 to 100 Kpa = 0 to 100% stroke.
If you want to use any other type of positioner a I/P will
not be necessary, since in electromechanical positioners the
I/P is already part of the positioner and obviously in SMART
positioners, the input to the positioner is 4 to 20 mA.
Good luck
| Is This Answer Correct ? | 24 Yes | 2 No |
Answer / vishal sharma
we need 250 ohm resistane because when we need to opearte
any loop eg.line pressure control loop er need to instal
pressure transmitter in line after control valve on that
time if we instal 250 ohm resistane in controller we dont
have to need another SMPS install for 24v signl to pressure
trasmitter for 2-wire system after install 250 ohm
resistance we recive 24v output trrough controller.
| Is This Answer Correct ? | 0 Yes | 4 No |
Answer / rohit
A electronics controller needs 4-20mA current and we have
230v or more voltage in industry so to maintain flow of
current 250 ohm resistance is vital.
I=V/R
| Is This Answer Correct ? | 2 Yes | 16 No |
what do you mean by Loop checking ? What are the cold loop check and hot loop check? what are the difference between these two loops?
HI FRIENDS IHAVE QUESTION 1.WHAT IS PARTIALSTROKE TEST?WHY IT IS USED ON ESD ON OFF VALVES?
What is two wire system and how it work
Can Any body tell me how to check Modbus Settings in ER300N L&T trivector meter?
how u meassure room temp?is it possible 2 meassure room temp by rtd or thermocouple?between rtd n thrmocouple which is more regard?3 meassure diff. between rtd n thermocouple?
Can any one tell me what type of question asked for instrumentation and control interview panel??? pls mail ramashankar.goel@gmail.com
PLS TELL ME THE FUNCTION OR PRINCIPLE OF CREEP RELEIF VALVE..
How can a d.p. Transmitter be calibrated?
Explain about relays.. Can we give both AC and DC to the same relay... How it is energising.. Explain its working..
Which type of pressure can be measured by these elements?
how to calculate density?
EXPLAIN NETWORK COMMUNICATION ON DCS?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)