How will you calculate the correct KWH value if your CT is 600/5 and your KWH meter is rated for 100/5



How will you calculate the correct KWH value if your CT is 600/5 and your KWH meter is rated for 100..

Answer / k.prakashchandra

If the load is 100 A ,the meter records correctly if the CT ratio is 100/5 as the meter gets 5A current . If the CT ratio is 600/5 the current in the meter will be 5/6 A for the same load current . Hence to get the correct reading ,multiply by 6.

Is This Answer Correct ?    8 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

Why lose 1 phase voltage in 33kv to 415v stepdown transformer

0 Answers  


Damping resistor provided in open delta (tartiary) winding of a measuring PT at the incoming of a MV inverter drive panel is getting heated up. Can any body explain the reasons and suggest the remedy?

0 Answers   Danieli,


What can be a rating of a transformer(KVA) if the load is about 1000KW?illustrate by showing formula?

2 Answers  


How to calulate cable size for 200KVA,160KVA& 40KVA load?

1 Answers   ABB,


What is primary and backup protection?

0 Answers  






Why DC current is not used in transformer?

20 Answers   JK Paper, TCS,


what do you mean by linear and bilateral network?

2 Answers  


why there is a phase shift lies between primary and secondary voltages of a transformer?

7 Answers   Mecon,


i need bhel question papers.

5 Answers   Bhel,


i am going to correct power factor of 1600kw induction motor,when i calculate capacitance of capacitor it is three time more in star connection than delta. if motor is star connected which connection i shall adopt for capacitors and reason for adopt this connection

0 Answers  


On monitor it is written that current rating is 2.2 Amps. Is it a monitor current drawing capacity or CPU & monitor. If it is only monitor rating, what will be the rating of only CPU and what will be the power consumption rating of PC, Monitor & Scanner? In net, I learnt that computer consumes only 200-300W while running. With the current rating of 2.2 Amps, how it could be 200-300Watts. Please explain?

3 Answers  


what is suroounding current of dg set?

1 Answers   Airtel, Sukarma,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)