How will you calculate the correct KWH value if your CT is 600/5 and your KWH meter is rated for 100/5
If the load is 100 A ,the meter records correctly if the CT ratio is 100/5 as the meter gets 5A current . If the CT ratio is 600/5 the current in the meter will be 5/6 A for the same load current . Hence to get the correct reading ,multiply by 6.
Is This Answer Correct ? | 8 Yes | 2 No |
Why lose 1 phase voltage in 33kv to 415v stepdown transformer
Damping resistor provided in open delta (tartiary) winding of a measuring PT at the incoming of a MV inverter drive panel is getting heated up. Can any body explain the reasons and suggest the remedy?
What can be a rating of a transformer(KVA) if the load is about 1000KW?illustrate by showing formula?
How to calulate cable size for 200KVA,160KVA& 40KVA load?
What is primary and backup protection?
Why DC current is not used in transformer?
what do you mean by linear and bilateral network?
why there is a phase shift lies between primary and secondary voltages of a transformer?
i need bhel question papers.
i am going to correct power factor of 1600kw induction motor,when i calculate capacitance of capacitor it is three time more in star connection than delta. if motor is star connected which connection i shall adopt for capacitors and reason for adopt this connection
On monitor it is written that current rating is 2.2 Amps. Is it a monitor current drawing capacity or CPU & monitor. If it is only monitor rating, what will be the rating of only CPU and what will be the power consumption rating of PC, Monitor & Scanner? In net, I learnt that computer consumes only 200-300W while running. With the current rating of 2.2 Amps, how it could be 200-300Watts. Please explain?
what is suroounding current of dg set?