when power transformer is flashed which gas is produce in
side?
Answers were Sorted based on User's Feedback
Answer / abbeer
Each of the fault result in thermal degradation of the oil
either alone or in combination with paper insulation. This
gives rise to the evaluation of various hydrocarbon gases,
hydrogen and oxides of carbon, in quantities depending on
the type of fault.
Heavy current arcing is characterized by the evolution of
significant quantities of hydrogen and acetylene (C2H2). If
the arcing also involves paper insulation, the oxide of
carbon will also be present.
Partial discharge usually results in evolution of hydrogen
and lower order hydrocarbons.
Localized heating or hot spot gives rise to methane and
ethane in appreciable amount.
Prolonged overloading or impaired heat transfer can cause
CO and CO2 to be generated due overheating paper
insulation.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / arunava
Hydrogen
O2
N2
Methane
CO
Ethane
CO2
Ethylene
Acetylene any of these.
Is This Answer Correct ? | 2 Yes | 6 No |
what is diffrances between fuse and breaker protection? which one is best?
what is second harmonic, how is effect transformer ?.
What is E.M.F ?
Is a DC Transformer Possible? if Yes, Then Why, if not Then Why?
upto how many load can v connect to stabilizer which is used for tv
what is vA rating and class of a ct.
what are the protection equipments used betbeen HT line and transformer in a power plant
For Eg a 30 kw motor at full load how much kw it takes And at no load how much KW it will take?
What should be the protection scheme for a 15kw, 3-phase motor working in a lathe machine.
which protection function should measure RMS value of current&DFT value of current?
What is the main uses of VCB & ACB?
DIFFERENCE BETWEEN NORMAL TRAFO AND THRISTER TRAFO?