what does mean ct knee voltage and burden
Answer / liladhar danej
VA BURDEN :
The apparent power of the secondary circuit in Volt-amperes expressed at the rated secondary current and at a specific power factor (0.8 for almost all standards)
knee VOLTAGE :
That point on the magnetizing curve where an increase of 10% in the flux density (voltage) causes an increase of 50% in the magnetizing force (current).
The ‘Knee Point Voltage’ (Vkp) is defined as the secondary voltage at which an increase of 10% produces an increase in magnetizing current of 50%. It is the secondary voltage above which the CT is near magnetic saturation.
| Is This Answer Correct ? | 1 Yes | 0 No |
How can we calculate the motor frame sizes?
How earthing/grounding done in aeroplanes and ships.
what is zinc diffusion?
In 2500kva transformer how much is the withstand High voltage power frequency between primary to secondary and earth? And secondary to primary and earth?
What is the meaning of utility ground and clean ground? How the distribution panel is grounded?
What is an infinite bus bar?
Why derivative controller is not used in control systems?
Is any generator is developed which is operated with out diesal or other expensive source?
what is the formulae of calculating voltage drop?
compressor compresses air means exactly what happens?
describe the Operation of induction generators from bus bars
which protection are used for turbo generator in thermal power plant.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)