what does mean ct knee voltage and burden 

Answer Posted / liladhar danej

VA BURDEN :
The apparent power of the secondary circuit in Volt-amperes expressed at the rated secondary current and at a specific power factor (0.8 for almost all standards)

knee VOLTAGE :
That point on the magnetizing curve where an increase of 10% in the flux density (voltage) causes an increase of 50% in the magnetizing force (current).

The ‘Knee Point Voltage’ (Vkp) is defined as the secondary voltage at which an increase of 10% produces an increase in magnetizing current of 50%. It is the secondary voltage above which the CT is near magnetic saturation.

Is This Answer Correct ?    1 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

What is the effect of solar radiation on the design of an Isolated Phase Busduct?

1874


how can calculation ate Amps for cabel. Ex-for 1sqmm wire hou many amps we can draw

1994


What is the polarization index value ? (Pi value)and simple definition of polarization index ?

765


Why the cores of large transformers build up of circular cross section?

1747


UG cable sizes were specified in sqmm. But practically its not coming to mesure. What's the reason for that? And how they specify the size of the cable?

1484








1663


Explain what is electric traction? Explain few advantages of electric traction system?

615


how flow current in 220 kv line to line

1544


what about electrical pannel.? What is meant by plc pannel.?

1878


which protection function should measure RMS value of current&DFT value of current?

1484


What is d main advantage of using double circuit 3 phase transmission ?

1430


exolain the star delta connection

2191


What is the Designing & Selection Procedure for a DG/Transormer of rated capacity?

1709


How does the slip regulator works as a startor

1505


how to check avr of dg set of 125kva

2155