why we need the starters for motors
Answer / sabaris
Normally motor takes current at the time of starting is three times of full load current.at this starting time there is no presence of back e.m.f. to compensate this effect of current.so,this much current will affect the motor windings results overheating... due to this we use starters to reduce the starting current at the time of starting..In running say 80% of its speed the back e.m.f. will generated.on that time the full vge is applied to the motor terminals to run its rated speed.
there are many starters are available depends upon the type the motor construction... i.e. star-delta,rotor resistance,autotransformer,2 point and 3 point starters,etc....
| Is This Answer Correct ? | 10 Yes | 3 No |
why are the maintaine power factor and how can this control and this is how work.
What is LT Breaker Panel?
which type of A.C motor is used in the fan (ceiling fan, exhaust fan, padestal fan, bracket fan etc) which are find in the houses ?
25 Answers Airtel, MPPTCL, USSA,
why the India electrical supply transmission loss is high when compare to us
what is the difference between pvc & fiber glass cables
Sir we have 12.5 MVA(110/11KV) transformer (Y-Y) connected,which tripped showing earth fault,when we charged transformer it stood OK ,but on connecting 11 KV feeders it tripped showing earth fault.our service engineers found that the B phase and R phase phase connecting to neutral broken from HV OLTC(on load tap changer),and R phase and Neutral is ok.Dissolved gas analysis shows that accetline content is high,tan delta value is 12.My dout is it is an internal fault of transformer,why REF or diffrential relay is not acted?
If auto trip is operated, can you close the breaker.
A 100KVA SINGLE PHASE TRANSFORMER 10000/200V,50HZ REQUIRES 300V AT HV SIDE TO CIRCULATE FULL LOAD CURRENT WITH LV SHORT CIRCUITED.THE INTAKE IS 1000W.THE % OF REGULATION ON FULL LOAD AT 0.8 PF LAGGING WILL BE HOW MUCH AND THE SECONDARY TERMINAL VOLTAGE ON 0.8 PF LEADING WILL BE
i m electrical diploma holder i want to do plc $ Scada some body tell me which insitute is best for me near chandigarh
how calculation to be done of cable size/o.h. conductor size of 11kv h.t.for the load of 2175 kw
what is the difference between equipment earth and system earth.
advantages of vvvf drives over non vvvf drives for EOT cranes
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)