When testing an earthing connection, we use a 60 or 100 candle bulb with a phase connected direct from supply and the other wire to the new earthing provided.If the bulb glows then the earth is ok.Else earth connection is not Ok.
So, why dont we can use all the home appliances taking a single wire from the phase and the return connection to Earth instead of return connection to neutral?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
100 W bulb draws about 0.5 A , hence the voltage drop for 5 ohm ER is about 2.5 V which is not noticeable . For 10 A load , the drop would be about 50 V .
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / karthick
Because, neutral volt is '0'v when the phase is increase neutral volt also increase so neutralvolt reduce though earth
Is This Answer Correct ? | 0 Yes | 3 No |
How damper winding in synchronous motor suppress Hunting?
if any body have question paper of railway (section engineering),then plz send me .i will thank of him/her.
what is the pulse and audio frequency transformer? what is different between induction regulators and tap changing transformer?
what different in delta & star connection in motor?explain
5 Answers Bhushan Power Steel, Hyundai, KPCL, L&T,
what does kirlosker deals with?
how can i find ct ratio of meter by seeing name plate of meter and how it should be used in MF calculation if it shows only-/1???
Please give me the formula stating relation between AC & Dc.
What happen if 200 KVAR capacitor connected to power continuesly?
What are the different towers used in 132kv transmission line? what are the differences between the P,R,S towers used in 132KV and detailed explanation
If the output of a 100kva, 415v generator is stepped up to 11kv with a 500kva transformer,can the transformer be Loaded above the source generator loading?
What is working of Trip Ckt.Supervision Relay?
dear all, i want to ask that what is diversity factor. please explain breifly. because i hve quiet no concept about this.