What is the difference between Error and Offset.
Answer / senthil ramanujam mohan
I can give you simple example:-
Consider a temperature controller(on/off valve),
setpoint - 100deg
Offset - (-4)
dead band - 2
ERROR - SETPOINT - ACTUAL VALUE
If temperature raises from 90deg>>>>94>>at >96degrees the
valve closes.this is becoz we have an OFFSET of (-4
degrees)(setpoint - offset value)
So,now the valve is closed.temperature drops down from
96degrees<<95<< at 94degrees the valve starts open.this is
becoz we have a DEADBAND of 2degrees.
Error(contrl valve):-
setpoint - 100degree and actual value - 90degrees.
temp range - ( 0 to 200)for error scaling(becoz
controller works from 0 to 100%)
error scaling = 100/200 - 0.2 which is multiplying
factor for error to the controller
Finally,
ERROR = [ SETPOINT - ACTUAL VALUE ] X ERROR SCALING.
[ 100 - 90 ] X 0.2
[ 10 ] X 0.2
2.
hope you guys understand.
Is This Answer Correct ? | 4 Yes | 15 No |
Why do we use triad cable for RTD to Temp.transmitter connection? Why we don't use 3 core cable?
1 Answers Process Control Technologies,
How does a redundant controller comes in line when the main controller fails??
what sud u do if u dont get feedback from control valve?
which transister (npn or pnp) is used in vibration monitoring for negative voltage?
what is the diffrence between plc&dcs
4 Answers HCL, Hindustan Zinc,
Transmitter reading is zero but in DCS showing one Bar what is the reason ?
Tell me the field calibration procedure step by step with diagram of pressure gauge, pressure switch, pressure transmitter, temperature switch, level switch, flow switch, flow transmitter.
What is the relationship between the universal gravitational constant (G) and the acceleration due to gravity (g)?
How we can check the 2 wire proxy switch? & how it is connected to DI MODULE OF PLC?
What is the difference between conductive lined pipe and conductive unlined pipe? Why do we see that?
0 Answers Process Control Technologies,
can someone tell me about electronic speed switch &how it conect with proximittyswitch?(with dgm)
Level in tank under vacuum (Ex: Condensate Tank of Power Plant)is measured using D. P. type level transmitter. Tank is subjected to vacuum of 755mmHg. Is it possible to fill wet leg ( i.e. leg connected to top of vessel with low point of D. P. xmtr) with water?. Are there chances of water getting sucked under vacuum? if yes, what is the solution?