Answer / mani
from dcs we give 4 to 20 ma to i/p converter. from i/p we give the 3 to 15 psi pnematic signal given to cv.
Is This Answer Correct ? | 23 Yes | 0 No |
Answer / bert
The type of signal going to control valve is either a
pneumatic or electronic signal. For a pneumatic signal its
3 to 15 PSI or 0.2 to 1.0 kg/cm2. For electronic signal its
4 to 20 mA.
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / abdulbasit137@hotmail.com
two types signal come control valve 1.pneumatic signal 3 to
15 psi (2)electronic analog signal 4 to 2o milla amp
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / parag pathak
Control Valve is final control element of clost loop. So
signal coming to control valve will be in pneumatic form
but depends on size of Valve. It can be 3-15 PSI or 0.2 -
1kg/cm2 but it is not fixed. There is one instrument called
Positioner which will convert 3-15 PSI signal to desired
siganl depending on Control valve.
For any Contol Valve signal will come from Control room in
the form of 4-20 mA. this 4-20 mA signal was converted to 3-
15 PSI signal by instrument called I/P converter. This
siganl will go to positioner and the positioner o/p is
given to valve actuator to get desired opening and closing.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rajkumar.diice
The signal type depends on
the location of control valve!
For explosive hazard area the
signal be pneumatic and be 3
to 15psi! The converters be
mounted in somewhat
distanted area! For all control
valves the signal be 4to 20mA
over 1to 5 volts from a
control room! For inbuild
current to pressure
converters control valves the
signal be 4to20mA over 1to
5volts dc
Is This Answer Correct ? | 2 Yes | 3 No |
Answer / susant
from dcs analog output signal 4-20ma dc provided to control
valve
Is This Answer Correct ? | 3 Yes | 6 No |
what is the function of a diaphragm?
Which boiler is use in power plant
WHAT IS DIFFERENCE BETWEEN TWO WIRE RTD AND THREE WIRE RTD?
what is function of PLC, and how is it work , explain with difination
1 Answers Bapco Bahrain Petroleum Company,
Can we use thermocouple in generator of power station replace RTD(pt 100)? if we don't have any place for use RTD.
What is cut off relay? And why use in PLC and DCS?
admittance level sensor meaning?
SIR MAY I KNOW IF RADAR TYPE LEVEL TRANSMITTER SHOWING IN THE FIELD 0 % LEVEL AND IN DCS SHOWING 100% THEN WHAT IS THE CAUSE I CLEAN THE CHAMBER & TAKEN ONLINE BUT ONLY ONCE ITS BECOME ZERO IN DCS BUT AGAIN 100% SHOWING IN DCS,THEN I REMOVE THE POWER SUPLLY AND CONNECT IT AGAIN .IS IT OK BUT STILL IN THE DCS ITS 100% AND ON THE DISPLAY ITS INITILAZIATION PLEASE HELP ME READRING THIS?
Flow tax range 0 to 100 mmh2o ,flow rate 40 tons /hr, I want change flow rate example 42 tons/hr so tx range ?
What is cable size for intrenal wiring in DCS or PLC ,from any card to Terminal amd Why
I want to measure bidirectional steam flow? Kindly suggest me a suitable flow meter. steam is superheated at 41kg/cm2, 350°C
Hi Frnds , If Suppose 1 Pair cable of 1.5 sq mm is used for Transmitter and instead of 1.5 sq mm if i used 0.5 sq mm cable will the resistance change will occur and does it affect our transmitter reading. plz mail ur answer to ntnkamble@gmail.com plz immediately mail ur reply