Answer / kk
It depends on the application where we use the same.
MCCB have adjustable tripping characteristics where MCB have fixed tripping characteristics.
MCCB is selected if it is incommer ,MCB is enough if it is O/g feeder
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / aditya shirbavikar
MCB is a gear where MCCB is a switchgear. MCCB may be said to be best if chose because, with an MCCB you get a current sensing relay for auto tripping during a fault.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / sunitkumarsonu
in this case mcb is better because mcb is much cheaper than the mccb.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / revanna
mcb is much enough becase load capacity is too low
so,insted of MCCB is better to using MCB becase low cast.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / seshagiri204
MCB is Simply a Mechanical Switch which makes or breakes the circuit by hand. In other words MCCB is a current sensing device which detects the abnormality in the circuit and trips the circuit. Today many of them are using MCCB only. And further As for as fault concern it is better to select MCCB
| Is This Answer Correct ? | 1 Yes | 0 No |
according to my experience, if load continuous current less or equal than 60A, it is better to use MCB, it is easy to install and cheaper. you can select MCB tripping class A,B or C depends on your application.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sahedul islam sagor
MCCB tripping Capacity is low when MCB. We know a machine starting current is high but its running current is normal if we used MCB it will trip instant with starting current but if we use MCCB it will take a little time for running machine.
| Is This Answer Correct ? | 0 Yes | 1 No |
Whether we used insulated line for 33KV supply. what we called it.
What is the difference between generator and turbo generator - related to power gereration
what is the maximum current rating in india for home?
in parallel operation of power transformer why the distance between power transformer and capacitor bank feeder is necessary to know
I have an 15A fuse MCB that controls a night storage heater. It needs replacing and is now obsolete. Is a 16A C curve MCB the correct replacement?
A 400KVA transformer has 400 Hz frequency. If the frequency is changed to 50 Hz, then what will be the new KVA rating?
Up to how much limit of HP of electric motor the Star- Delta Starter can be used ?
What is main difference between earthing and neutral grounding?
In industries Power factor is maintained by installing a suitable KVAR bank, How is the PF maintained for domestic use, where is the capacitor bank connected
what is the multi strand cable size? 0.45mm is area of one strand & 370nos of strand.
In a poly phase circuit if clamp on meter shows same load on three phases and their sum on neutral then why we use three and a half core cable or maximum the same size of core as that of phase?
I WANT TO KNOW LONGFORM OF CT/PT USEDIN POWER PROJECTS OR HT SWITCH YARD.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)