Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


if you asked to choose a ckt breaker from MCB & MCCB for 32A
which one will be best and why??

Answers were Sorted based on User's Feedback



if you asked to choose a ckt breaker from MCB & MCCB for 32A which one will be best and why??..

Answer / kk

It depends on the application where we use the same.
MCCB have adjustable tripping characteristics where MCB have fixed tripping characteristics.
MCCB is selected if it is incommer ,MCB is enough if it is O/g feeder

Is This Answer Correct ?    9 Yes 1 No

if you asked to choose a ckt breaker from MCB & MCCB for 32A which one will be best and why??..

Answer / aditya shirbavikar

MCB is a gear where MCCB is a switchgear. MCCB may be said to be best if chose because, with an MCCB you get a current sensing relay for auto tripping during a fault.

Is This Answer Correct ?    2 Yes 0 No

if you asked to choose a ckt breaker from MCB & MCCB for 32A which one will be best and why??..

Answer / sunitkumarsonu

in this case mcb is better because mcb is much cheaper than the mccb.

Is This Answer Correct ?    2 Yes 1 No

if you asked to choose a ckt breaker from MCB & MCCB for 32A which one will be best and why??..

Answer / revanna

mcb is much enough becase load capacity is too low
so,insted of MCCB is better to using MCB becase low cast.

Is This Answer Correct ?    2 Yes 1 No

if you asked to choose a ckt breaker from MCB & MCCB for 32A which one will be best and why??..

Answer / seshagiri204

MCB is Simply a Mechanical Switch which makes or breakes the circuit by hand. In other words MCCB is a current sensing device which detects the abnormality in the circuit and trips the circuit. Today many of them are using MCCB only. And further As for as fault concern it is better to select MCCB

Is This Answer Correct ?    1 Yes 0 No

if you asked to choose a ckt breaker from MCB & MCCB for 32A which one will be best and why??..

Answer / nur.asidik

according to my experience, if load continuous current less or equal than 60A, it is better to use MCB, it is easy to install and cheaper. you can select MCB tripping class A,B or C depends on your application.

Is This Answer Correct ?    0 Yes 0 No

if you asked to choose a ckt breaker from MCB & MCCB for 32A which one will be best and why??..

Answer / sahedul islam sagor

MCCB tripping Capacity is low when MCB. We know a machine starting current is high but its running current is normal if we used MCB it will trip instant with starting current but if we use MCCB it will take a little time for running machine.

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

Whether we used insulated line for 33KV supply. what we called it.

1 Answers  


What is the difference between generator and turbo generator - related to power gereration

1 Answers  


what is the maximum current rating in india for home?

3 Answers  


in parallel operation of power transformer why the distance between power transformer and capacitor bank feeder is necessary to know

0 Answers  


I have an 15A fuse MCB that controls a night storage heater. It needs replacing and is now obsolete. Is a 16A C curve MCB the correct replacement?

2 Answers  


A 400KVA transformer has 400 Hz frequency. If the frequency is changed to 50 Hz, then what will be the new KVA rating?

0 Answers   Spectrum,


Up to how much limit of HP of electric motor the Star- Delta Starter can be used ?

1 Answers  


What is main difference between earthing and neutral grounding?

3 Answers   Jindal,


In industries Power factor is maintained by installing a suitable KVAR bank, How is the PF maintained for domestic use, where is the capacitor bank connected

3 Answers  


what is the multi strand cable size? 0.45mm is area of one strand & 370nos of strand.

1 Answers  


In a poly phase circuit if clamp on meter shows same load on three phases and their sum on neutral then why we use three and a half core cable or maximum the same size of core as that of phase?

1 Answers  


I WANT TO KNOW LONGFORM OF CT/PT USEDIN POWER PROJECTS OR HT SWITCH YARD.

7 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)