Answer / jithin
VCB is designed for HT it has vaccum chamber that prevents arcing and it triping speed is higher
ACB is desined for LT the terminals are almost open to atmospere it can cause flashing if we use it on HT
| Is This Answer Correct ? | 32 Yes | 0 No |
Answer / karna
HT Line Means 6.6KV,11KV and 33KV. LT Line means 415V. So
the ACB are Manufacutered for LT side because , based on
shortcircuit KA busbar terminal are designed in ACB . In HT
line while switching On & OFF ARC will be more it will not
withstand in ACB . IF we use VCB in LT side , the VCB will
not helpfull at fault condition, because its upstream
breaker will trip or component will damage
| Is This Answer Correct ? | 17 Yes | 5 No |
Answer / maurilio
if you use a VCB in low tension it odes not make problems
but if a ACB or Air Circuit Breakers in HT you will see a
lot of ligthning and probably fire in the breaker
So it is no convenient to use a ACB on HT
| Is This Answer Correct ? | 13 Yes | 8 No |
Answer / sushil kumar
Vcb is ht supply use rating of high voltage but acb lt supply used this manufacture 440 voltage difference for relay siting vcb and acb vcb is use closed area but acb use open area
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / hardik
As per Karna ACB is not usfull in HT because of its limited
capacity but in casw of VCB apply in LT it can dafinatly
helping out after making its ragular reliese setting and
tripping in foulty condition is depend on relay... so VCB
we can use but drow back is VCB in LT system it is more
expancive then ACB thats it...
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / kishore
actually acb is made for LT bcz EVERYTHING HAVE A LIMIT,SIMILARLY IF WE USE VCB AT LT THEN NO PRBL BUT IT IS A GREAT ECONOMIC LOSSES FOR US OK.
| Is This Answer Correct ? | 2 Yes | 3 No |
30 kVA and voltage 380/220VAC how to find out kA?
can we use 220 volt 15 w a.c. lamp on 220 volt d.c.
Difference between a pilot wire and a normal conductor?
0 Answers United Arab Aluminum Company,
What would be the size of wire used for 2 Ton of window A.C?
whay is snubber circuit , why we are using snubber circuit in thyristor
how ups works ? various parts of ups and working principle
how to male a d.c bettery to blow a 230v bulb?
a battery is having capacity 100AH and 25% charging .if a load taking 10A & connected 6 hour .what is the final condition of the battery.
roles of owslaw explain?
all interview questions with answers of ntpc (2000-2009
why do we prefer -48 volt instead of -24volt or -12 volt etc. ??
If we connect capacitor in series DC supply so what happened?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)