We use ACB in LT and VCB in HT.But if we use VCB in LT and
ACB in HT that what will be the effect on the system or any
power range?
Answers were Sorted based on User's Feedback
Answer / jithin
VCB is designed for HT it has vaccum chamber that prevents arcing and it triping speed is higher
ACB is desined for LT the terminals are almost open to atmospere it can cause flashing if we use it on HT
Is This Answer Correct ? | 32 Yes | 0 No |
Answer / karna
HT Line Means 6.6KV,11KV and 33KV. LT Line means 415V. So
the ACB are Manufacutered for LT side because , based on
shortcircuit KA busbar terminal are designed in ACB . In HT
line while switching On & OFF ARC will be more it will not
withstand in ACB . IF we use VCB in LT side , the VCB will
not helpfull at fault condition, because its upstream
breaker will trip or component will damage
Is This Answer Correct ? | 17 Yes | 5 No |
Answer / maurilio
if you use a VCB in low tension it odes not make problems
but if a ACB or Air Circuit Breakers in HT you will see a
lot of ligthning and probably fire in the breaker
So it is no convenient to use a ACB on HT
Is This Answer Correct ? | 13 Yes | 8 No |
Answer / sushil kumar
Vcb is ht supply use rating of high voltage but acb lt supply used this manufacture 440 voltage difference for relay siting vcb and acb vcb is use closed area but acb use open area
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / hardik
As per Karna ACB is not usfull in HT because of its limited
capacity but in casw of VCB apply in LT it can dafinatly
helping out after making its ragular reliese setting and
tripping in foulty condition is depend on relay... so VCB
we can use but drow back is VCB in LT system it is more
expancive then ACB thats it...
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / kishore
actually acb is made for LT bcz EVERYTHING HAVE A LIMIT,SIMILARLY IF WE USE VCB AT LT THEN NO PRBL BUT IT IS A GREAT ECONOMIC LOSSES FOR US OK.
Is This Answer Correct ? | 2 Yes | 3 No |
What kind of battries are generaly used with Disel Generator?
what is the reason of current flow in nutral although load is balanced (three phase equal current)
Why the meters sonnected to metering core of CT are not damagedon event of a fault??? Explain the phenomena??
please give me all the Alarm .Trip ,Safety Relays & Conditions of Chiller mail me on ashokbabunhce@gmail.com
raleigh method
dear all, in motor operation , motor is of 100 hp and bimetal relay setting is 130 amp, if relay is getting tripped on 120 amp balance current what can be the reason? Relay is newly replaced. I dont know but is there any frequency effect in thit case? Can frequency variation affect bimetal relay operation?
why number of stator and rotor slots are not equal in IM?
WHY PROTECTION CT IS USED NEXT TO METERING CT?
i karmveer bharti persuing b.tech . plz send me syllabus and name of reference books. for preparation of section eng.
what is the difference between watts and volts?
can we coorect P.F. OF 320 KVA ALTERNATOR AT LOCAL SITE WITH RATED .8 PF LAGGING.
What is D check in a Diesel generator for 1000kva DG