30 kVA and voltage 380/220VAC how to find out kA?
Answers were Sorted based on User's Feedback
Vipul Kumar your answer is wrong.
W is not = 1.732x380xI. W =1.732x380xIx PF. You left off
the power factor
Bala your answer is wrong also.
KA is not equal power/ (1.732*400*% of Impedance)Note
spelling of impedance. Where did you go to school?
Amps = 30 KVA/ (0.380 x 1.73)or 30000 va/380 x 1.73
Amps = 46
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / simon
30Kva=30,000va
30,000 VA=440V*68.1818 Amp*1 (Pf)
Hense Ka=0.068
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / vipul kumar rai
W=1.732x380xI
30x1000=1.732x380xI
I=30000/658.16
I=45.581 ( FOR THE PRIMARY CURRENT )
W=1.732x220xI
I=78.731 ( FOR THE SECONDRY CURRENT )
Is This Answer Correct ? | 1 Yes | 3 No |
Answer / bala
we need to know the Impedance of the TxR.Becos the Formula for Determine the KA value is
=power/ (1.732*400*% of Impedence)
For EX-
Power = 1500 KVA
Voltage = 400V
Impedance = 6%
short circuit = 1500*1000/(1.732*400*0.06)
= 36085A or 36 KA
Is This Answer Correct ? | 0 Yes | 2 No |
Why consumers are charged based on Kwh basis why not on Kvah basis.
what is the difference between LLL and LLLG fault ?
how to varied the frequency in transmission line and how i kept it as a constant one?
why we use to transmit the power in three phases intead of single phase ?
can you send me the placement papers of electrical engg. from companis like NTPC,DRDO,IOCL,HPCL,BPCL etc.?If,plz send as soon as possible.Thanks.
what is photo voltic cell,& what are the materials associated with that?and any spcifications like volts/cm etc?
Explain the function of VFD
what will happen if the prime mover on the field excitation of the on-coming generator fails?Explain.
0 Answers Ahsanullah University of Science and Technology,
In a ordinary plug can we hold the earth in hane and connect the circuit to supply?will we get a shock?
what's the activities of reactor in Buchholz relay?
Explain difference between stand by earth fault and residual earth fault protection?
What are test values for an 63 KVA and 100 Kva Distribution Transformers for the following typical tests 1)Magnetic balance 2)Short circuit test 3)Open Circuit test 4)Vector group confirmation test .please give me the standard values for all the above tests.