what is the meaning of Ring Mean Unit in a substation or
trasformer also tell me its oerpuse?
Answers were Sorted based on User's Feedback
Answer / sreejim sreedharan
RMU (Ring Main Unit) is of two types. TRM (Triangular Ring
Main Unit) & QRM (Quadrilateral Ring Main Unit). TRM is (2
Feeder+ 1 Transformer Feeder) and QRM is (2 Feeder + 2
Transformer Feeder). RMU is mainly used for redundancy of
feeders. Sometimes it is difficult to get the Municipality
plot approval for a new Substation. In such cases we go for
a RMU as per requirement. There are 3 Feeder, 4 Feeder & 5
Feeder RMUs.
Hope it helps you. :)
Is This Answer Correct ? | 115 Yes | 4 No |
Answer / hesham
RMU IS used to feed the transformer from two different feeders within ring
1- TRM ( two incomer and one outgoing feeding only one transformer 2+1 )
Or ( 1+2 ) one incomer and two outgoing feeding two S/S.
2- QRM ( 2+2 ) two incomer and two outgoing feeding two transformer
or ( 1+3 ) one incomer and three outgoing feeding three s/s.
Is This Answer Correct ? | 19 Yes | 5 No |
Answer / shafi
RING MAIN UNIT IS DISTRIBUTION OF ELECTRIC POWER TO
DIFFERENT LOAD OR FEEDER, IT IS CONSISTS OF SF6 BAKER, ONE
INCOMMER AND TWO OUT GOING FEEDER
Is This Answer Correct ? | 22 Yes | 11 No |
Can a transformer be used as voltage or current amplifier?
what are the disadvantages in GIS over AIS
How to configure the drives in PLC, through Profibus commnication. And to how to address it?
If an electrical component has a positive temperature coefficient, how come such components have high power losses due to heat if current decreases when resistance increases? assuming power given by I^2*R whereby the Resistance is infinite.
Three way plug point is there ,in that plug why we need earth pin is bigger than compare with phase and nutral pins?
State ohm’s law?
how can calculate static 3phase 4wire CT & PT operated energy meter constant when calibrating using refference meter suppose we have 11kv/110v PT and 30/5A CT, the meter constant is 160imp/kwh, where meter is showing MW energy? give me solution which constant i feed in my refference meter for calibration of energy meter?
what is working of no & nc.
What is maximum rating of transformer ?
75kw drive operated motor current fluctuation from(85-130)ampere.current setting in drive is 130amp.sometimes motor trip when current limit cross 130amps.I change the drive. still current fluctuate between 80-130amps but in this time motor not trip,current setting in drive is 130amps.where is the problem?
How do you think they do earthing or grounding in ships and aeroplanes?
is it necessary for 200 kva transformer to have marshaling box and cu plate earthing for neutral