How to calibrate electronic type level switch low?
Answer / carl_ellis
Calibrating a point level switch
Contact level switches detect the presence or absence of
the medium, whether solid or liquid, by direct contact with
the medium. The switch output for most devices is an
on/off binary signal that reflects the presence or absence
of the medium. Some level switches use a 4-20mA output
that does not modulate, the current signal is either 4mA or
20mA, depending its detection state.
Most level switches offer some form of sensitivity
adjustment (depends on the technology) and some have an on-
delay or off-delay adjustment of the output relay trip,
used to avoid nuisance trips.
Calibration consists of
- testing whether the switch output changes state when the
presence or absence of the medium is changed and adjusting
the sensitivity setting for the specific medium used with
the switch.
- whether the on-delay and off-delay settings comply with
the requirements of the installed application
Depending on the technology, there might be sensitivity
adjustments or on-delay or off-delay adjustments, which are
specific to the installed application, and a calibration
would cover.
A non-contact level switch, like Siemen ultrasonic ULS200,
can be tested in place by comparing the reading with a
physical distance measurement (tape measurement) or out-of-
process by shooting against a solid target and measuring
the distance to check the trip and reset setpoints.
Carl Ellis
Measure First
Is This Answer Correct ? | 2 Yes | 0 No |
what is use single seated and double seated valve?
2 Answers Doha Petroleum Construction DOPET,
what are the definitions of input, output, command & signal according to instruments controlled by PLC using DCS System?
what is the basic principal of vertax flow meter
3 Answers Balrampur Chini Mill, Saba,
HI THIS IS NOOR AHMMAD.SHAIK, I AM WORKING IN INSTRUMENTATION MAINTENANCE Dept. in BOILER HOSE(BHEL HYDERABAD),,any other persons are working in same dept. i want some HELP in my subject
A valve in series with an orifice plate (DP transmitter), is aligned for constant pressure in the pipeline, if there is an error dx, How to align it in process.
hi all plz tell me difrence between analog or digital load cell.
Tell about your IFFCO plant visit.
what is differential pressure transmitter and transducer? how to work?
what is mapping in instrumentation and control engineering
How to calibrate radar type level transmitter for interface level? Total liquid(liq.1 and liq.2), level both the liq individually? For. Both the liquid levels how the signal will go from transmitter to dcs? How to calibrate. Single radar 9:26:55 AM for 2 different liquids in a tank?
0 Answers Almeer Technical Services,
what is control valve input and out put
How many interlocks at turbine? Plz explain briefly
0 Answers MRPL Mangalore Refinery and Petrochemicals Limited,