How to calibrate electronic type level switch low?
Answer / carl_ellis
Calibrating a point level switch
Contact level switches detect the presence or absence of
the medium, whether solid or liquid, by direct contact with
the medium. The switch output for most devices is an
on/off binary signal that reflects the presence or absence
of the medium. Some level switches use a 4-20mA output
that does not modulate, the current signal is either 4mA or
20mA, depending its detection state.
Most level switches offer some form of sensitivity
adjustment (depends on the technology) and some have an on-
delay or off-delay adjustment of the output relay trip,
used to avoid nuisance trips.
Calibration consists of
- testing whether the switch output changes state when the
presence or absence of the medium is changed and adjusting
the sensitivity setting for the specific medium used with
the switch.
- whether the on-delay and off-delay settings comply with
the requirements of the installed application
Depending on the technology, there might be sensitivity
adjustments or on-delay or off-delay adjustments, which are
specific to the installed application, and a calibration
would cover.
A non-contact level switch, like Siemen ultrasonic ULS200,
can be tested in place by comparing the reading with a
physical distance measurement (tape measurement) or out-of-
process by shooting against a solid target and measuring
the distance to check the trip and reset setpoints.
Carl Ellis
Measure First
| Is This Answer Correct ? | 2 Yes | 0 No |
Hi, I'd like to know the purpose of MOS (maintenance override switch). At site, these switches are installed in a stanchion with the transmitter (connected to ESD). thank you.
3 Answers Adani, Adani Wilmar,
Explain about safety integrated level protection? . How it was differ from other protections ?
Can we use a 10000 Lph Flow Transmitter in 100 LPH flow line to get 20mA O/P by adjusting SPAN ?
what is upstream and downstream in liquid flow?
what is ment by PID controllers? explain with example?
How do you calibration D.P transmitter? ?
I have a steam flow DP transmitter that has output swinging. Steam valve is in manual.I have good steam pressure. The impulse lines have steam tracing on them. The steam tracing has a hole in it that is blowing raw steam on the high side impulse line only. Could this be causing the swinging?
I have a LT of 10000mmwc range. can i use this LT in 1000mmwc range of tank?? if yes than what happened???
how many types of sensor in instrumentation
how to calculate control valve bonnet size?? or how to select its material?
Can any body help me,The GE Mark V control system is windows based or Dos based?
how to turbine speed measurement?
0 Answers Jindal Steel and Power,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)