I have a LT of 10000mmwc range. can i use this LT in 1000mmwc range of tank?? if yes than what happened???
Answers were Sorted based on User's Feedback
Your tx's range is 0~10000mmwc if u
use it at 0~1000mmwc head press tank
than it will indicate 10% level when tank
full. So just calibrate it (configure it) at
0~1000mmwc before take inservice for
actual reading of tank at output
Is This Answer Correct ? | 17 Yes | 3 No |
Answer / ys
u can use this transmitter. but u should rerange the
transmitter.(ie if tank service is water and ur lt is dry
leg type,then LRV=0 and URV=1000MMH2O.. If ur lt is wet leg
calibrated, then LRV= -1000 AND URV=0 MMH2O)
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / carl_ellis
I have a LT of 10000mmwc range. can i use this LT in
1000mmwc range of tank?? if yes than what happened???
A change from a range of 10000 mmwc to 1000 mmwc is a turn
down of 10:1
If your transmitter supports a minimum range of 1000 mmwc
within the accuracy spec you require, then re-range the
transmitter and use it.
Most smart DP transmitters from major manufacturers will
support this.
Carl Ellis
Measure First
Is This Answer Correct ? | 1 Yes | 0 No |
Square root calculation for dp flow transmitter?
What is difference between “Fault Tolerant” & “Fault avoidance” PLC? Application where these system s are used?
I m appointed as an automation trainee engineer in small firm in that I am only the one , my company give me a project on s7-200 as i m beginner I don't know how to program so please send me the helpful site so that I complete my project before deadline....please help me out in this critical situation.
what is the difference between Feedback controller and Feed forward controller. and when it is to be used.
Name four general (not technical) criteria that would you consider important, when deciding upon a particular control valve?
How comparison of objects is done in PHP5?
How 2 calibrate level tank having large height..?
what is dedband in instrumentation ?
What is the difference between instrument earthing and normal earthing? and why is it necessary to do so?
why use squareroot in flow measurment by dp transmitter?
what is the principle of ultrasonic flowmwter and radar type flowmeter?
what is function of sensor, and how is it work , explain with difination
0 Answers Bapco Bahrain Petroleum Company,