Good Evening all.My question is - For a feed water line to
an equipment if i need to measure the flow we will use
orifice /magnetic/vortex depend on cost/spec.If i need to
measure a ''Alarm''signal and ''Interlock'' from one point
i think we can use orifice type in one location with 2
different tapping points - one for alarm and one for an
interlock to flow valve..If in case i need to have both
these signals(Alarm & interlock) from magnetic flow
meter,is it possible??will 2 seperate sensors will be
located inbuilt r we can program it ??..i thk we can have
one transmitter with these 2 signals...need to know any
technical issues are there?pls clarify
Answers were Sorted based on User's Feedback
Answer / carl_ellis
If this is not SIS (safety instrumented), the 4-20mA from a
single flow transmitter can feed a separate I/O modules (4-
20in, relay out) an alarm module and a separate interlock
module.
Or, depending on the converter/transmitter model, most
magmeters have at least one assignable relay output, some
have two relay outputs.
I've always used orifice flange unions that have only one
set of taps. There might be a double tap flange unions, or
I suppose you can drill and weld the pipe for taps. But
again, unless this is SIS, why would you? Decisions made
on a 4-20mA flow signal on a PLC?DCS/Controller/I?O modules
can do multiple functions.
If your situation is SIS, you should state that.
Carl Ellis
Measure First
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / carl_ellis
It seems you are using a flow meter's relay(s) to generate
alarm signals at various amplitudes: low, low/low, hi,
hi/hi.
The flow meter doesn't really use these alarm signals
itself, rather it generates the alarm signals and provides
the alarm signals to other devices, for whatever purpose,
alarm, annunciation or an interlock.
There might be a flow meter with 3 alarm relays. I don't
know. That's a shopping issue.
Most places will use a PLC, a controller or a DCS to
generate alarms from the analog flow signal.
But if your flowmeter doesn't have enough relays, then use
a "DC alarm trip" I/O module with the flow meter's 4-20mA
analog output.
The modules have an analog input and one or two relay
outputs with adjustable setpoints. There's probably a
dozen models on this page:
http://www.api-usa.com/signalconditioners_alarms.php
These I/O modules are not used "in a magmeter", they're
external I/O modules.
They place a small burden resistance in the 4-20mA circuit,
need an enclosure and AC or DC power to operate, but they
accomplish the task of providing multiple alarms at various
setpoints.
The 4-20mA signal is wired in series with the I/O module
and any other receiver devices.
Carl Ellis
Measure First
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / thiagaraj
@CARL ELLIS.. Thanks for your response.In case of using
Alarm (or) Interlock it was a normal practise that we
use ''LOW''LOWLOW'' (OR) ''HIGH''HIGHHIGH'' signal in the
same instrument(orifice etc)..If i need to
use ''LOW''HIGH''LOWLOW'' in the same Instrument is it
possible to use these 3 alarms in a single instrument(flow
transmitter )..If yes is it can be used in Magnetic flow
meter ..pls state its advantages and disadv also.pls clarify
Is This Answer Correct ? | 0 Yes | 1 No |
As an industrial instrument technician what we have to know?
What is Positive Calibration and Negative Calibration?
flow transmitter range is 0 -500 mmwcc but the transmitter shows 12 ma for o mmwc instead of 4 ma ...how to solve this problem when we apply 375 mmwc it shows 16 ma
any body please send me the old question papers of ongc test.
what is the difference between RS 232,RS 485,RS 422, how they different from each other
d/p flow transmitter LP side give to pressure.what you geting out put ? how you get(ma)?
what step is taken for ESD ( emergency shut down) in DCS REPLY to hashimka20009@gmail.com
0 Answers Bosch, Eskom, Sabic,
in sulfur process what is material of impulse line we use to connect with transmitter ? and does teflon affected by sulfur?
How do we MEASURE OR CALCULATE VELOCITY used to calculate REYNOLDS NUMBER??
how is work pressure switch& level switch?what is the principle of this?
what is gas metering system? gas chromatograph? and gas compressors?
-200mmwc to 500mmwc range transmitter have there 4mA is -200 and 20mA is 500.what is the range in 12mA?