A 30KW motor running at 1450 rpm draws 56A, how would you
determine if this is correct or not?
Answers were Sorted based on User's Feedback
Answer / divakaran a
P=1.732xVxIxP.F
30KW=1.732x415xIx0.8
I=30000/(1.732x415x0.8)
I=52.17 AMPS
sO the current drawing from the motor is 52 amps (Theoriticaly)
in practical the motor may draws more current as based on the load.
Is This Answer Correct ? | 13 Yes | 2 No |
Answer / vipul kumar rai
P=1.732xVoltage x I(current )xPower Factor
30KW=1.732x415xIx0.8
I=30000/(1.732x415x0.8)
I=52.17 AMPS
as per thory 52.17A current draw.
so 56A is approx correct.
Is This Answer Correct ? | 2 Yes | 0 No |
what is surge suppressor?
why the efficiency of the dc machine is high ,when it is operated as a generator?
what is diffrent of RCCB & MCCB
In what condition the HT fuse breakes?
what is starting current and use of starting current?
How much difference can there be between HT & LT KWH unit consumption at the same load?
What is Electrical Grade Aluminum for Tubular BusBars. i am confused between 6063 and T6 or T5 and what is BS 2898 and BS 159?
What is the normal earth resistance?
Can we convert off load tap changer transformer to on load tap changer transformer
Am using an electronic digital display to see the RPM of ABB ACS 550 drive, which is showing negative value when the motor & drive in stop mode but it is showing correct value during the run mode. can anyone help me out??
2 Answers Bala Power Solutions,
Which are the major Nuclear power accidents in the world?
Is it reuired to use house service barcket for 31/2 core 300 Sq.mm cable,if the distance between pole & shop is around 2 mtrs only or can I hang the cable with GI support in air? upto what size of cable GI serrvice btacket is necessary?