yokogawa Temperature transmitter showing Error 15 which is Reverse Cal Fail (confirmation calculation result is bad) in manual they mentioned reasion That the output goes to the value set by hardware failure mode jumper. How can solve this problem ? anybody can say solution
Answer / carl_ellis
In the manual (from which you cited) the user action for
error 15 is 'contact service personnel'.
You can try that, but I suspect that it means, for all
practical purposes, replace the transmitter. I don't know
if Yoko offers a spare 'puck' that can be replaced in order
to salvage the housing and display, or not. You'll have
to ask.
You might try cycling power to it to see if an electrical
spike on the loop wiring adversely affected the processor,
and cycling the power might re-initialize it, but the
likelihood of success is very small.
When a transmitter goes to fail-safe mode, it's usually the
last act of the last performance, the actors are clasping
hands, and taking a final bow before the show closes.
tell 'em Carl sent you
Is This Answer Correct ? | 3 Yes | 0 No |
Actual using of tube bender to bend 2 opposite 90 deg at correct measurement center to center of tubing.
how to calculate the temp. of RTD&Thermocouple when we got some mV r Ohms?if anybody has d chart pls mail the chatrs to me...
calibration of instruments.
Which mechanical device is used in pressure gauges to reduce pulsating
how u calibate pr tx without master tx?
Difference between guide wave radar & non guide wave radar ?
what is difference between positioner and position transmitter in control valve
my temperature transmitter in field showing 700 degree , whereas in dcs showing 459 degree, how to resolve this?
what will happen if transmitter wire get shoted?
In VVVF DRIVES VOLTAGE IS ALSO VARY WITH THE FREQUENCY. HOW? WHAT IS THE DIRECT FORMULA RELATING THESE TWO.
I am using 971 Enraf radar level transmitter for LPG tanks ,the tank side indicator gives the error code 999999999FL can any body give me any diagnostic for this issue?
Troubleshoot to the device level basic process control systems given the Process and Instrumentation Diagram?