A DP Endress and Hauser flow transmitter is always tripping
pump at low flow. set point is 74 cubic meter/hr. Thorough
impulse line flushing and zero calibration has been done,
yet problem persists. What do you think is the problem and
how do you rectify this fault?
Answers were Sorted based on User's Feedback
The stated question assumes that the design criteria for a
low flow alarm SP at 74m^3/hr is valid. It is not clear
whether the problem is limited to the instrumentation
without a clear statement that the pump has been determined
to be operating properly. Since this is an instrumentation
exam, I'll assume the problem is in the instrumentation.
If the instrumentation is the problem, then the DP's
indicated DP/flow rate has to be lower than the alarm SP.
What can cause a DP transmitter to indicate a lower
DP/flowrate than it should?
If the equalizing valve is not tightly closed or leaks at
the valve seat, the DP will be lower than it should be as
the DP approaches zero, depending on the leak rate.
Damaged orifice plates read low, resulting in low indicated
DP readings.
Lower line pressure than the "design" line pressure will
reduce the indicated DP reading.
Someone changed out the orifice plate (OP)with an OP with
bigger bore or re-installed the correct OP backwards.
Since DP operation is "high side pressure minus low side
pressure equals indicated DP", a leak anywhere on the high
side will reduce the high side DP pressure and result in a
low indicated DP. That could be
- leak in the high side impulse line or its fittings
- manifold valve flange gasket leak on the high side or on
the process side
- vent leak
(however liquid leaks are usually visually evident)
In a mis-configured system, the PLC/DCS might have square
root extraction in addition to square root extraction on the
DP transmitter, which would cause a low flow rate indication
at the PLC/DCS.
Tell 'em Carl sent you.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / mohamed
You should see the time delay of the alarm itself and the time lag of the transmitter
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / mukesh singh
increase the tripping time,your transmitter might be malfunctioning..follow the trend of DP.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ntia
Check the strainer of your pump..remember that your pump supplies the pressure...if the pump strainer is dirty...it will be be giving low flow and since your dp was set to shutoff the pump at a low flow..then your dp will continue to shut off the pump until the pump is cleaned and the fault is rectified.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / samir
If it is a malfunction of flow transmitter then you should cross check with portable ultrasonic flow transmitter. Whether it is showing correct or not. & then you can follow previous advise.
| Is This Answer Correct ? | 0 Yes | 0 No |
How to do manual mapping in radar type level transmitter?
Coal mill Instruments Equipments for cement plant And process diagram ?
1. How can leveltrol be installed in steam drum for measuring the level of steam drum?
i have 20 kw motor & my vfd drive capcity is 18 kw if possible to use 20kw motor on this vfd?
Why we are using DPT(Differential Pressure Transmitter) in separator instead of level trasmitter?
why level transmitter input is given 4to20ma
why we use -ve voltage in vibration monitoring system.generally we use 4 to 20 mA as output of instrument then why we use voltage in vibration
why I need valve guard and whats different between guard and positioner ??
what is fire and gas system?
2 Answers Andhra Petrochemicals Limited,
what is the procedure of O2 sensor(ABB) calibration?
We have ZR22G-100-S-A-E-T-T--E-A/CV/F1 Model Zirconia Oxygen analyser which is Yokogawa make. I kept the analyser in Flue gas path at Air pre heater area. My plant is 7.5MW Biomass power plant. For a particular fuel, Coconut Husk which contains Sodium and Potassium chlorides iam not getting proper reading, Analyser output always Zero. I calibrated the analyser and it is OK. For Other fuels like Wood chips, Cholam waste, DOB, Groundnutshells, Ply wood waste and all iam getting actual percentage of Oxygen. What is the main reason behind this draw back?
what is sliding spool valves?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)