if field commnictor 475 does not communicate with transmitter
what will you do ?

Answers were Sorted based on User's Feedback



if field commnictor 475 does not communicate with transmitter what will you do ?..

Answer / mallu byali

We have to conform before connecting the hart communicator
into tx whether it is smart family or not if may other then
connect the resistance series into the its terminal do the
calibrate.

Is This Answer Correct ?    10 Yes 1 No

if field commnictor 475 does not communicate with transmitter what will you do ?..

Answer / carl_ellis

1) Check for 24Vdc? Yes, but assuming the power supply is
24Vdc, don't expect the voltmeter to read 24v, unless you're
back in the control panel where the power supply is.

If you're out in the field where the transmitter is, you are
not close to the (-) side of the power supply, so where do
you put the black voltmeter probe? The only place for it
on the transmitter's (-) terminal, but measuring voltage
across the transmitter's (+) and (-) terminals only shows
what the transmitter's voltage drop is, not what the source
voltage is.

There is the voltage drop across all parts of the loop, the
transmitter, the load and the wiring. So checking voltage
across the transmitter's (+) and (-) terminals will never
show a full 24Vdc because of the voltage drops in the loop.
With short wiring runs and a 250 ohm load resistor, the
voltage across the (+) and (-) transmitter terminals might
be as high as 23V @ 4.0mA output, but could be as low as 10V
with a 20mA output across 500 ohms.

2) Checking to confirm that the transmitter is a smart
transmitter is a good idea. There are protocols other than
HART or Foundation Fieldbus (Honeywell's DE), and there are
lots of 'dumb' transmitters, too.

Some brands, like Siemens, allow HART to be enabled or
disabled, so the transmitter may be HART capable but have
the HART comm disabled.

3) Connecting a resistor in series is a good idea if the
load resistor is an unknown.

The article at the link below tells why a HART loop needs at
least 230 ohms of resistance

http://blog.lesman.com/2011/10/06/add250-ohm-resistors-to-make-hart-work/#more-68


The temporary use of a 250 ohm resistor is typical because
they're so common in a process plant.

4) Is the HART device at address 0 (zero)? The
communicator can talk to any address, but when connecting
point-to-point on home run wired transmitters, the
expectation is that the transmitter will be at HART address 0.

5) Experience will show that there are the inevitable
problems like
- broken or corroded communicator leads or clips that can go
'open' or be intermittent.
- power supply ripple or EMF induced noise on the loop
circuit can conflict with HART's 1200 baud FSk digital
communications
- some loop device, like a loop isolator or HART-unfriendly
loop indicator has stripped off the HART signal with a low
pass filter, leaving only the 4-20mA current signal
- wrong version DD so the communicator will connect but only
perform the so-called "common commands".

Tell 'em Carl sent you.

Is This Answer Correct ?    1 Yes 0 No

if field commnictor 475 does not communicate with transmitter what will you do ?..

Answer / abu maryam

In my opinion there are several causes of this problem:
1- Check the power source if it 24 volt or not.
You should disassemble the power source if it is 24 on out side and still 24 after connecting to device this mean that the power source is good but if it is 24 volt out side and zero after connecting this mean there is found problem in power source (may be problem in module).
2-Read device data if it support hart protocol or not.
3-Disassembled device and connect separate power source and connect 250 ohm series if it no benefit added change the resistance from 250 to 1000 ohm and try or disassemble the resistance and power source and apply power source from multi function calibrator which has internal resistance then try to connect.
4-May be device support hart but hart property is disabled by definite internal jumper in device so we should change this jumper according to device manual.
5-May the device support hart its data files is not added to hart communicator for 1 of the following 2 reasons:
the first:hart communicator is not updated.
The second:the device data filed is not added to hart communicator and it need its special programs and its special cable as found in foxporo transmitters.
6-May the connectors or cables has problem so use another cable.

Is This Answer Correct ?    0 Yes 0 No

if field commnictor 475 does not communicate with transmitter what will you do ?..

Answer / marut_tripathi

first check 24 vdc power have or not in transmitter.
termination proper or not of transmitter.

Is This Answer Correct ?    1 Yes 2 No

Post New Answer

More Instrumentation Interview Questions

where do you give the 4-20 ma i/p in a MIL control valve?

3 Answers   Siemens,


How to calibrate radar type level transmitter for interface level? Total liquid(liq.1 and liq.2), level both the liq individually? For. Both the liquid levels how the signal will go from transmitter to dcs? How to calibrate. Single radar 9:26:55 AM for 2 different liquids in a tank?

0 Answers   Almeer Technical Services,


what is the relation between flow and pressure.for example relationship between level and pressure is p = phg like that i want ans for this question.and also how to calculate orifice sizing and flow transmitter. pls some one ans for this questions.

3 Answers   Orchid, SRF,


How to calibrate level transmitter with use of HART?

0 Answers   Samsung,


What is DeltaV?

2 Answers  






what is different between modbus and serial link? please could anybody give right answer.

2 Answers  


How to calibrate electronic type level switch low?

1 Answers  


WHAT IS THE VALUE OF MICRON

2 Answers  


Hi i am aneesh, done btech in applied electronics & instrumentatiin. And then i took mba in finance & marketing.After that i got placement in finance co and worked there for 3.5 yrs.Now i wanted to come back to engineering job.But without engg experience, i may not able to find an opening.i have done a course related to flow meters and ite calibrations. Kindly suggest where should i try to get a job?

0 Answers   Qatar Petroleums,


generally transmitter power supply having some range(12v to 35v) but the out put(4-20 mA) must same for given input.If we vary the power supply voltage then output mA also to be change according to V=IR. Is there any voltage regulator in the transmitter ?

2 Answers  


How to calculate 47Liter H2 Gas cyilnder consumtion? Cylinder inlet Pressure is 200bar and Discharge pressure is 6.0bar. Flow is 100ml/min.For the above condition how many days one cylinder can be used?

1 Answers  


what is "smart" in smart transmitter ?

4 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)