For an 100kw generator, only 50kw of load is connected. Will
the generator generate only 50kw or 100kw. If it generate
100kw what happens to rest of the 50kw. What happens if we
connect more than 100kw of load?
Answers were Sorted based on User's Feedback
Answer / kj
The answer above is correct in that the generator will only
generate power as required.
The limiting factor with load above the 100kw in the
example is the power output of the engine. If excess load
is applied the frequency will drop until underspeed
protection shuts the genrator down or the engine stalls.
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / balwinder
Any capacity Generator will not generate full power at all
times, According to load requirements it will give power. For
50kW load the 100kW generator will generate 50kW only.
There is no problem if we connect more than rated power in
small amount but it cause over heating of generator.
| Is This Answer Correct ? | 6 Yes | 3 No |
diff between grounding & earthing
8 Answers BARC, Mobiserv, NTPC, Tata Steel Limited,
why PT transformer primary r the grounded?
During he starting up of the motor, the upstream's MCCB (350A) always trips due to the UVT relay activated. Can Star-delta starter use for a 20kW Motor (For a powder mixer machine) cause voltage-dip in the supply line voltage? If so, what are the recommended solution to eliminate/reduce the transient voltage dip in the line voltage?
DIFFERANCE BETWEEN function of ELCB? function of rccb? function of mccb? function of acb? function of mcb?
How CT is connected to measure current by changing plug setting , ratio is 300 - 150 / 5 A ?
1 Answers Ajanta Pharma, Bhel, Cosmo Films, Suzlon,
what is the difference between MCB & MCCB
How to connect the chemical earthing and complete process tell me plz
any one have papers of hpcl or sailof ELECTRICAL ENGG.
what is the responsibilities of electrical project engineer?
Explain and give examples about VCB?
0 Answers AZ Engineering, Vodafone,
how gen. load increase or decrease ? what happen with gen on that time
Why does the power consumed is always constant even if a fan speed is altered?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)