For an 100kw generator, only 50kw of load is connected. Will
the generator generate only 50kw or 100kw. If it generate
100kw what happens to rest of the 50kw. What happens if we
connect more than 100kw of load?
Answers were Sorted based on User's Feedback
Answer / kj
The answer above is correct in that the generator will only
generate power as required.
The limiting factor with load above the 100kw in the
example is the power output of the engine. If excess load
is applied the frequency will drop until underspeed
protection shuts the genrator down or the engine stalls.
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / balwinder
Any capacity Generator will not generate full power at all
times, According to load requirements it will give power. For
50kW load the 100kW generator will generate 50kW only.
There is no problem if we connect more than rated power in
small amount but it cause over heating of generator.
Is This Answer Correct ? | 6 Yes | 3 No |
percetans
what is the cable capacity of any load wise .
I have experienced electrical maintenance HT ,but I completed be ECE ....can I apply c license or not ???? Pls help me friend s...
how to check the 3ph capacitor is good or not.
14 Answers MacLellan, Yash Technologies,
what is the AC Plant and how can do the work with parts and picture tell us 150 Tr
Can I Drain A Oil For Sample When The Transformer is Running? (Charged)
if the load is reactive then what is the use of calculating the real power and what is the use of reactive power if my question is wrong please excuse me..
in 3 phase (4 wire) star connection - is current pass through neutral??
WHAT HAPPENS IF FUSE IS CONNECTED TO NEUTRAL WIRE
why contactors are used ...? is contactors and relays are same ...?
I have a shop heater with a 1/3 hp capacitor start, induction motor driving the fan. Intermittently, the fan motor speeds up significantly for several seconds (15-60 sec) then slows to normal operating speed. The manufacturer suggested changing the capacitor which made no sense, but I did it to no avail. Could this possibly be caused by the centrifugal switch intermittently reconnecting the start winding?
How can we find the breaking capacity of a Load breaker switch (LBS) fed from 11 kv supply??ex:50KA, 26kA etc???detailed step vice answer pls.